I have two adjacent light switches sharing a box. Live black wire comes from house control panel to the box. Then, presumably, each of the other two wire inputs into the box go one each to an interior light and an exterior light.
The problem is that when I connect only one of these "dead" blacks to the live black from the control panel, the third black then also has power; however, neither light comes on and the two switches are not operating independently. I have not modified the wiring in any way since the house was built. Any suggestions as to why it may have been wired in this way AND how to fix this (short of rewiring)? Thank you!
15
  • Does either of those switches have a mate? That is can either light also be controlled by a switch in another location? Sounds like some messed up 3-way switch wiring, but we’re going to need clear pictures of all the boxes involved showing what’s connected where to be able to help sort things out.
    – Tyson
    May 15, 2018 at 22:25
  • Both switches are mate-less.
    – Paul
    May 15, 2018 at 22:29
  • How do I post a photo?
    – Paul
    May 15, 2018 at 22:30
  • Not sure how your accessing the site, there’s an icon for photo upload on most devices. If you can’t figure it out upload to imgur.com (you don’t need to create an account on imgur.com you can do simple upload just by clicking upload), once you have an imgur.com link just paste it into a comment here.
    – Tyson
    May 15, 2018 at 22:34
  • It looks deceptively simple inside the box. Live wire from control panel up the middle, two outfeeds (one on either side). Live piggybacked to the individual switches. The two outfeeds on the outward ports of the switches. However, the two outfeeds appear to be coupled.
    – Paul
    May 15, 2018 at 22:37
Start by looking at your technique
What I see in the photo is a lot of wires in a slight spiral with the ends nibbled a bit from having been in a wire nut. I also see all the screws snug, which tells me you are using the backstab holes. A few things about backstabs:
  • They are single-use, once you pull the wire out (even with the release) their spring strength is gone and they cannot be used again. You can't ask more from four springs that are only a small part of a receptacle that costs 50 cents in total.
  • The wires being twisted and serrated (from prior use in wire-nuts) means they won't work with the backstab regardless, and they also look a bit short for typical backstab length, so these may be combining to make you think they're in, when they're not. Don't cut the wire ends off - read on.
  • Also, even if used perfectly (straight wire, virgin stab) backstabs are highly flaky and unreliable, and give most of us no end of grief. (not least, side pressure on the wire can unwind the spring force or lift the wire off the contact blade, and that can happen when shoving wires back into a box).
  • The real purpose of backstabs is to allow high-production builders (who wire 10 houses a week) to work faster. That's not really applicable to the home DIYer.
The best play (generally) is Stop using backstabs altogether and doing so might solve the problem right there. Switch to the screw terminals, form a J-hook on the wire and hook it over the screw terminal (clockwise so tightening the screw tightens the J-hook, that's not Code, just works better, you'll see). The screw will flatten out prior bends and wire-nut serrations because it has a large area and a lot of clamping force.
I'd also undo the white wirenut and inspect the wires. Make sure they have enough copper exposed for an effective wire-nut splice. Ideally follow the instructions that come with the wire nut, but I aim for a strip length of about 75% of nut length. It will "suck in" as you tighten the wire nut, and be firm with that. Also inspect the white wires closely for any broken wires, as that would cause your symptom.
The symptoms say "lost neutral"
Lights not working and energizing either trailing hot lighting up both hots, that has "lost neutral" written all over it. Neutral current is unable to return to the panel, and that means the neutrals are also "going hot" (via the bulb filament). That's carrying hot over to the other lamp's neutral, through its bulb filament and back to the other hot.
It's also possible you are just seeing capacitive coupling from the cables running parallel for a stretch. This capacitive connection isn't capable of providing any useful current, so it cannot light a neon-light tester or move the physical needle on a traditional analog voltmeter. However DVMs and powered hot detectors will detect it, which can make you crazy.
If it remains a mystery, you might also try hooking only one lamp's hot and neutral direct to supply hot and neutral - when you turn the breaker back on, that lamp should light - and then check other wires for signs of life. If you are seeing capacitive coupling (or parallel induction), then the other lamp's hot and neutral will both show voltage, since both are disconnected, yet connected to each other via the lamp filament.
  • I just tried the idea of removing one neutral and hot from the circuit entirely. (I'm also skipping the switches altogether at this point.) With either side connected to the control panel line-in I get indication of power to the appropriate lamp, but apparently not enough to power the lamp.
    – Paul
    May 16, 2018 at 16:38
  • @Paul and you are turning the breaker on at the panel? It may be a wire issue at the panel, and the phantom voltage is on the supply. May 16, 2018 at 16:42
  • Yes. Switching power on and off at the panel.
    – Paul
    May 16, 2018 at 16:47
  • Messing with anything at the control panel is beyond my comfort zone because that switch/breaker also controls other outlets and my garage door opener (none of which have ever been glitchy). I have an electrician coming this afternoon. Thank you for all your help!
    – Paul
    May 16, 2018 at 17:04
    @Paul fair enough, personal minimums are a huge part of safety. May 16, 2018 at 17:09