I'm going to ask a power raise. I'm moving from 3kW + 30% (15A) to 4,5kW + 30% (25A).
I'd know if my main feed (3m, 2,5mm2) is enough to hold the new max rate.
EDIT: I've checked my main feed and it's actually 4 mm^2, not 2,5.
  • Where are you? UK, US (unlikely, given metric measurements), somewhere else? – Martin Bonner supports Monica Aug 20 '19 at 17:15
  • I'm in Italy. Thank you Stack Exchange for having me to write unuseful stuff! "comments should be at least 15 characters". – DDS Aug 21 '19 at 14:39
  • The right way to have answered my question would have been to edit your original question to include the info - not to write a comment at all. – Martin Bonner supports Monica Aug 21 '19 at 16:18
2.5 mm2 is equivalent to #14 for us Americans, which is required for use on 15 A circuits (or a larger wire). On a 20 A circuit, you need (at least) #12 [4 mm2], and for a 30 A circuit (the next step up for your 25 A needs), you need #10 [6 mm2].
So, given your current wire size of #14 [2.5 mm2], you cannot increase the capacity of the circuit at all.
  • Thanks, Actually I'm on a 4mm^2 (I checked the wire mark) that I taught it was 2,5mm^2. So I'll go for 4 kW+30% (20A) instead of 4,5+30% (25A) and I'll be safe. – DDS May 3 '18 at 13:09
  • Keep in mind American wire ampacity ratings are quite conservative compared to EU ratings. Look at an old copy of NEC table 310.16, and remember those too are conservative. – Harper - Reinstate Monica May 3 '18 at 14:11
  • To reiterate Harper's point, in the UK a 30A fitting only needs 4mm². See tlc-direct.co.uk/Book/6.3.3.htm – Martin Bonner supports Monica Aug 20 '19 at 17:16
  • @MartinBonner UK-style ring circuit or normal "radial" circuits? – DDS Aug 21 '19 at 14:41
  • The link is to a section titled "The radial circuit". You can use 2.5mm² on a ring circuit - but the (not particularly convincing) justification is that the socket is fed with two wires. – Martin Bonner supports Monica Aug 21 '19 at 16:20