In my detached garage, there is a ??/3 cable (haven't measured to know the gauge, though I'm thinking it's 10..) coming into a fuse box with two circuits. The strange thing is, the third conductor is cut and not being used. The black wire is powering one circuit, and the white is powering another. Both circuits have 30 amp fuses. Is this setup safe? I believe in the main box, there is a double 60 amp breaker powering the garage, but I'm not sure the configuration (it's been a couple months since I've looked at it).

I'm preparing to do some electrical work (add a few outlets and lights) and wanted to make sure I didn't burn down my garage. I was planning on using 12 gauge wire, and put the lights on one circuit and the outlets on the other. I plan on replacing the fuses with 20 amp.

As a side note, if this is a 10/3 cable, is it possible to have 240 in the garage? What kind of amperage could this support if the same cable was powering two 120v circuits?

Sub Panel Sub panel in garage

Main Panel Main Panel

UPDATE

Following the advice from the answers listed here, I did a bit of rewiring. The cable run to the garage had no markings on it, but based on a rough measurement using my wire strippers, I'm fairly confident the wires are 10 gauge. I disconnected power and tied the red wire to the ground and verified there was continuity, then got to work. I purchased a 2 pole 30 amp breaker for the main box, along with some wire nuts, a spool of 10 gauge wire, and some fuses.

From what I found online, wire nuts are code compliant inside panels, so I decided to forgo the junction box, since there was a little slack in the cable. I extended the red wire in the main box, and relocated the white wire to the neutral bar. Inside the fuse box, I verified that the "neutral bar" and box were not in contact with each other, then removed all ground wires and connected them with a wire nut. I extended the red wire and hooked it to one of the circuits. Unfortunately, the white wire was not quite long enough to reach the neutral bar, so I had to extend that as well (with red wire, since that's all I had at the time. I plan on replacing this once I get some white wire). Finally, I replaced the 30 amps fuses with 20s, since the wiring in the garage is 12 gauge.

enter image description here

I'm definitely open to comments about my work, seeing as this is the first time I've done something this extensive. I believe it's much more code compliant than before (aside from the red wire extending the neutral, the box not being grounded, and the open hole at the top of the box). If anyone notices anything in the attached photo, please feel free to let me know.

Thanks to everyone who provided input!

  • If you have two hot lines coming in, and no neutral going out, the garage must have it's own ground. Why they would use the white and no red for a hot seems questionable. – JimmyJames Apr 27 '18 at 20:49
  • 1
    @isherwood Right, and if you have 3 wires plus a ground, why wouldn't you use the neutral? As long as the two hots are on different phases, you just need the one neutral, right? – JimmyJames Apr 27 '18 at 20:51
  • 1
    /3 cable has several meanings. In flexible cords for appliances, ground is counted so /3 means black white ground. In fixed wiring in buildings (e.g. Romex, NM, UF, USE etc.) the ground is not counted, so /3 means black white red ground. We need to know which. – Harper - Reinstate Monica Apr 27 '18 at 21:08
  • @Harper In this case there are 4 total wires: black, red, white, and ground. In the photo I linked to, you can barely see the red wire as it was cut off. – Clint Warner Apr 28 '18 at 0:38
  • @JimmyJames That's what I was wondering... If the red wire is there why use the white if it's going to be hot? Unfortunately, a lot of work done on my house seems not that well thought out. – Clint Warner Apr 28 '18 at 0:39
4

This is no good

What's happening right now is that the bare grounding wire in the 10/3 feeder cable is being abused as a neutral by someone who clearly didn't know any better (as no-grounding-conductor feeders have not been Code for new installs for a while now). You're going to need to re-terminate the cable (and probably use a box to splice some extra length in at one or both ends) and use it properly (black for one hot, red for the other hot, white for neutral, and bare for ground) in order to make this safe and Code compliant.

Also, if this is run using 10/3 cable and being fed by a 2-pole 60A breaker, then it's vastly over-breakered, and that breaker will need to be replaced with a 2-pole 30A unit while you're at it with this.

Now that you've mostly fixed it...

There's one last thing I'd like to point out, and that's the thing that looks to be a hole in the bottom left corner of the cutout box. That hole should be able to take a 10-32 machine screw and pigtail, which you can then bundle in with the rest of the ground wires to ground the box.

  • At one time this was legal and common, no? Or have I just seen it often enough to think so? – isherwood Apr 28 '18 at 2:00
  • @isherwood -- 3-wire (no EGC) feeders to separate structures were permitted in prior Code editions (don't have a precise date tho). Rather daft to take the right cable and install it in the wrong way, though... – ThreePhaseEel Apr 28 '18 at 2:39
  • 1
    No, this was always bootlegged ground. Whoever did this was drunk, or just really, really doesn't care about safety. There's such a thing as ungrounded wiring, but this is not that. – Harper - Reinstate Monica Apr 28 '18 at 3:19
  • @Harper -- my best explanation for what the prior Code was doing was allowing the "bootlegging" because it treated a feeder to an outbuilding as equivalent to a service. Nowadays, we all agree that it's not :> but that logic took a while to trickle down to folks. – ThreePhaseEel Apr 28 '18 at 3:25
  • 1
    @isherwood I'm baffled with cutting off the red. Whoever did this knew enough to make it work. You have the wires, why not just use them? Is this something you've seen? – JimmyJames Apr 29 '18 at 23:43
2

Change the main panel breaker to fit the wire run

Start by finding out what size of wire this is. Now the main panel breaker size needs to be changed to match the wire. The job of that breaker is to protect the wire, and the electrical cabinet downstream.

  • #6 wire is good for 60A
  • #8 wire is good for 40A
  • #10 wire is good for 30A
  • #12 wire is good for 20A
  • The ampacity of the fuse box enclosure should be listed on a label.

The breaker in the main panel must be small enough to protect both the wire and the fuse box.

Get access to the red wire

You need to install an intermediate box e.g. directly above the fuse box. Bring the /3 cable into this new box, and get access to all the wires. Then extend the wires on down into the fuse box. You must make splices inside a junction box.

I would get another junction box such as a "4-11/16 deep square box" and a close nipple, and use the close nipple to bolt it directly to the fuse box. Make it so they clamp directly into each other, to cover up that extra hole.

Noting the fuse box does not appear to have separate neutral and ground bars, I suspect the fuse box is not proper for this purpose, and is actually designed to supply an A/C unit (which has no neutral). Disconnect all the wires from the central neutral area, and measure resistance to the box casing. If it's infinity, then you can use that as your neutral bar, and if you followed my advice with the close nipple, you can make all your ground connections there with a wirenut, pigtailing to the box's grounding screw (a #10-32 tapped hole).

Or you can go a completely different way here. Given your ambitions you may want to replace the fuse box with a proper subpanel. This will give you a separate grounding and neutral bar, provided you select your subpanel carefully. Don't go too small on the subpanel, a 60A circuit (if that's #6 wire) can power a lot of stuff.

  • Everywhere I read #12 wire is only good for 20 amps, is this incorrect? – Clint Warner Apr 29 '18 at 14:09
  • @ClintWarner whoops, that was my typo. – Harper - Reinstate Monica Apr 29 '18 at 14:22