I am adding a new outlet but want to make sure it is correctly grounded.

I have outlet A that I am going to be creating a new outlet B. I tested A and it says it is grounded and want to ground outlet B the same way. How do I see how outlet A is grounded and do the same as B if there is no grounding wire?

I am assuming that it is grounded through the metal outlet box. enter image description hereenter image description here

  • I don't understand your second paragraph. How will the old outlet be part of the circuit? – isherwood Apr 23 '18 at 14:16
  • 1
    I disagree that it’s a dup of that question, but it’s very likely a dup of something else. The way I read this OP’s question he that he has existing outlet A, which tests that it has a good ground—the wiring method is unclear but it must likely be conduit or metal clad something to provide ground. He wants to extend the circuit from outlet A and add a new outlet B, using /2 with ground. We also don’t know if current outlet A has a bootleg ground, which is another possibility. – Tyson Apr 23 '18 at 14:41
  • Should the question be more of how do I know how outlet A is grounded so I can ground the new outlet b the same way? – jokim Apr 23 '18 at 14:55
  • @jokim yes. At a very minimum if my assessment is correct you could re-write the question using A and B to make it easier to understand. I can see how a quick read now causes confusion. – Tyson Apr 23 '18 at 15:05
  • Can you look in the back of the box to see what the wiring method is? Wires going into multi-conductor cable that is clamped? Or disappearing into a pipe? – Harper Apr 23 '18 at 15:24
0

You can Install a GFCI outlet that has an 'equivalent' protection to be used in outlets where PE is not present.

0

You appear to have metal shielded cable ("bx cable") to the box.

In some jurisdictions, the metal jacket of the conduit is or used to be an acceptable ground.

Consult an electrician to verify.

0

The box is grounded, just not well

While the armor of old type BX cables does not meet modern grounding standards, it is grounded, so it's best that you use it instead of ignoring it. A self-grounding receptacle (it will have little clips on the yoke that bear against the mounting screws) should be used here, and the ground wires in any cables you are running from there should be made up to a ground screw on the box.

  • What does downstream cables mean? – jokim Apr 24 '18 at 2:35
  • @jokim -- any new cables that you're running from that box. – ThreePhaseEel Apr 24 '18 at 2:44
  • The new outlet is going to be inside a cabnet, does the metal box need to be inside the wall or ok to just screw it inside the cabnet? – jokim Apr 25 '18 at 13:02
  • @jokim -- that should be a new question :) – ThreePhaseEel Apr 25 '18 at 22:43

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.