Mine is a 3-phase German household. Main panel serves the kitchen and a 5 conductor 10 mm^2 with each phase fused 16A (w/ Hager FS) to the secondary panel upstairs. This services 6 rooms, a bath, and attic w/ 10A FS and a 3 phase CDA440D FI (RCD).

How should I make the connection at this secondary panel to another secondary panel servicing the garage? Specifically, what is the right device or connector to bridge two service lines? The panel is a Hager Volta 1P30 3-row, 36 unit. The 5 conductor 10 mm2 input from main panel must feed the 5 conductor 6 mm2 output to the next secondary panel.

The ground/PE/green-yellow should just share the PE bus.

I assume each RCD servicing the upstairs rooms should have its own neutral/null/blue bus. Thus, I need a separate neutral connector.

The 3 phases (L1,L2,L3) could be connected via switch (Hager SH363N), or Hager KC325? Or is another series fuse better (Hager MBN316A)?

5
  • Do you intend to have the garage panel to be secondary to the not-kitchen panel, or the two panels to be effectively side-by-side? Commented Apr 8, 2018 at 19:35
  • Are you sure your first subpanel is fused 16A? 10mm2 and 6mm2 wire are both wildly oversized for 16A. Oversizing wires is a good thing though. If you are willing to size the overcurrent protection in the main panel to a value allowed for 6mm2 wire, I see no need for overcurrent protection in subpanel #1 for the run to sub #2. We yanks call that a "through lug". Commented Apr 9, 2018 at 2:27
  • @ThreePhaseEel Garage panel will be secondary to the not-kitchen panel, i.e. in series. Main -> secondary -> garage. Commented Apr 9, 2018 at 10:28
  • @Harper I am very sure the first subpanel is fused 16A. The "electrician*", insisted on 10 mm^2 to the secondary and 6 mm^2 to the garage. I had originally 5x2.5mm^2 to the garage, which he made me replace with the 6 mm^2. * I fired my electrician for connecting 240VAC to the outside temperature sensor of my furnace, destroying the control module. Inexcusable incompetence. Plus his work was sloppy. Commented Apr 9, 2018 at 10:35
  • A stopped clock (12 hour analog) is right twice a day. We want electricians to be right a lot more often than that, but large wires there was a good call Commented Apr 9, 2018 at 14:51