I am installing a new wall light switch timer, but in addition to my ground, Hot, and Neutral wires that are currently running to the old switch, this new one requires a "Load" wire too. I tried wiring the neutral and load together, and it "Kind-of" works, but the four light fixtures now flash, this is with LED lamps in each socket.

Any ideas or suggestions for the Load wire, or the flashing lamps?

  • 2
    "load" is the lamp – jsotola Mar 4 '18 at 20:21
  • Can you post a photo of the inside of the back of the box? – ThreePhaseEel Mar 4 '18 at 20:34
  • Presumably the line cable enters in the switch box, is that right? That is, do you have in the switch box BOTH an always hot (the line hot, which is usually a black wire) and a line neutral (usually white)? – Jim Stewart Mar 4 '18 at 21:21
  • This is for back porch lights, that I am wanting to automate, there is one hot (121 volts by meter) one neutral, and a common ground, the box does not photo well because of the second back porch light switch that uses the same hot. When my new timer turns on it has a clicking sound like it has a solenoid in it, and the four lights on this switch now blink with the clicking noise – David Bourn Mar 4 '18 at 22:25
1

Is this in a bathroom? Do you want this timer to control a light or to control an exhaust fan?

In either case, the load wire is that wire to the light or fan (the load) which will be switched to hot when you turn on the switch and which will be automatically switched off at the end of the timed period.

I assume here that the line cable enters in the switch box so you have a neutral in the switch box. If the line cable enters in the load box, then you almost certainly do NOT have a neutral in the switch box and you will not be able to install this new switch without running a new cable.

The load must also have a neutral connected to it. This is so that all that is needed to "complete the circuit" is for the timer switch to switch on the line hot. But the load and the neutral must NOT be connected to each other.

Your new timer evidently also requires a neutral connection to it which your older timer may not have required. The neutral from the line cable and the neutral to the load (usually both white) will be connected with a wire nut in the switch box. Remove the wire nut and add a short pigtail white to the other two and twist back on the wire nut (so then 3 white wires would be under the nut). This pigtail supplies the neutral required by the new switch. This pigtail may be a provided lead on the switch or you may have to use a short piece of wire with white insulation.

With the old type timer switches if one would do this, it would trip the breaker. If you did this and it did not trip the breaker, then maybe these new switches have a built in protection against a wrong connection.

  • Jim, you are correct, i have a Load wire, not a Neutral! the switch does not work when I do not have the wire the switch manufacturer labeled Neutral hooked up to the same Load wire in the box – David Bourn Mar 4 '18 at 22:31