UPDATE: Problem has been resolved. The solution was checking the connections in nearby junction boxes on the same circuit to determine that a neutral connection had become loose.


I have a junction box in my house that (I thought) connect a hot line with a remote switch (near the junction box but on the other side of the wall) and a ceiling lighting fixture. The ceiling fixture is difficult to access.

My goal was to add an an electrical outlet where the junction box is. When I connected the outlet, I had 120V on both the neutral and hot (relative to ground) so I knew I had done something wrong. When I tried to reconnect the fixture the way it was, I couldn’t get the light to turn on. Here is how I thought the fixture was originally wired:

There are three romex cables coming into the junction box. When they are all disconnected, only one hot had 120V (relative to ground). That hot was connected to another romex cable hot going up to the fixture, the neutral from the fixture romex was connected to the hot on the switch romex, and the neutral from the switch romex was connected back to the neutral on what I’ll call the “panel romex”. I was able to tone out the switch romex with my multimeter to identify it. This was how I THOUGHT it was wired. Though when I reconnected this way, no light. I then tried switching things around so that the power was going to the switch first, and then fixture, still no power. In that case, there was 120V on the neutral wire after it had come back from the fixture.

I then completely bypassed the switch, thinking that the fixture should be permanently on, still no light at the fixture. Replaced the bulb in the fixture, still nothing.

Testing the voltage between the “panel romex” hot and neutral, I’m getting 40V, which seems strange to me. I’m thinking that I am not understanding how this is wired, and perhaps the “panel romex” is actually coming from the fixture or elsewhere? Right now, everything is disconnected and everything else in the house seems to be fine. Any idea what could be going on, and should it technically be possible to put an outlet at the junction box?

Thanks in advance.

Edit: junction box photo Photo of the junction box. I used different color wire nuts for clarity, and attempted to wire the box how it was originally wired. The red wire nut is connecting "panel" to "fixture", the yellow wire nut is connecting "fixture" to switch, and the blue wire nut is connecting switch neutral to "panel" neutral

15
  • Can you post photos of the insides of the boxes involved? Mar 3, 2018 at 6:41
  • In your paragraph three, you indicate that the hot on the panel romex tests to 120V. In your paragraph five, you indicate that the hot on the panel romex tests to 40V. Did I read you correctly? Mar 3, 2018 at 9:13
  • Try connecting a test load, such as a table lamp or work light, to the panel romex. Mar 3, 2018 at 9:13
  • @A.I.Breveleri I added clarification to my post. I'm getting 120v from the "panel" romex hot to ground, and 40V from the "panel" romex hot to "panel" romex neutral. I'm calling that the panel romex because its the only wire I'm getting 120V on when everything is disconnected, but like I said in my earlier post, I definitely could be wrong about that.
    – Alex
    Mar 3, 2018 at 17:38
  • @A.I.Breveleri I just connected and outlet to the "panel" romex and plugged a lamp in. Was only getting 47V at the grounded outlet, and the lamp wouldn't turn on.
    – Alex
    Mar 3, 2018 at 17:45

1 Answer 1

1

When I see an odd voltage like that I think of the two usual causes: (1) ghost voltage reading and (2) floating neutral.

Ghost voltages are commonly caused by induction from nearby live wires and will disappear when a load is applied. Try connecting a lamp where you had the voltmeter. Try between hot and neutral, between hot and ground, and between neutral and ground.

Floating neutral would be caused by a break in the neutral somewhere in that panel romex. To test for it switch off all the loads on the same circuit breaker, and then measure the voltages at the panel romex again.

"Panel" hot to "panel" neutral: 43V, "panel" neutral to ground: 6.5V, "panel" hot to ground: 120V - doesn't really add up, does it? Either the neutral has a varying intermittent bad connection, or something is interfering with your voltage measurement process. You'll have to examine the entire run of the "panel" romex to find the fault.