27
Background Info: My house is all electric.
Last month when I got my electric bill, I flipped. It was triple that of any month prior. Now I know the cold (heating) can affect this so I decided to turn my thermostat back, even though I never had to before. I've finally got the results back and to my surprise, it's still pretty darn high (but somewhat lower thankfully). The head-scratcher is that not only did I turn my thermostat down 4-6 degrees, it also hasn't been very cold here lately. It has ran a fraction of what it did the month prior, and that's just from the ambient temp difference. This isn't considering the fact that the thermostat is off for half of the day while I'm at work. I also wouldn't deem my system extremely inefficient, as I have a heat pump.
Anyways, so I'm suspecting there's something else at play here. Perhaps another large appliance like the washer/dryer, dishwasher, hot water heater, etc. However, I do not know how to troubleshoot this or determine how much energy any one appliance is using.
Are there any pro-tips or easy/cheap ways that I can measure, or at least get a general idea, of which appliance in my house could be causing such high energy usage? I've seen before meters that you plug into the wall (in-between the socket and appliance), but I imagine those are not the most inexpensive route to take. I was wondering if maybe I could see the real-time load for the entire house? Like at the meter, and then I could one-by-one disconnect appliances and notate the fluctuations in total usage.
Anything like that would be great, or if you have better ideas, please share!
Quick Note: I recently had someone move into one of my spare rooms. One of my suspicions that I'm looking to verify is that they take extra long showers and overwork my hot water heater. I mainly suspect this because they mentioned that they ran out of hot water, something that has never happened to me before.
I wouldn't be concerned if I was still considered "efficient" by my electric company, but as you can see, I went from being relatively efficient to not even close. enter image description here
UPDATE 3/3/2018 After doing some testing, I've come to realize that my heat pump isn't putting out any heat at all. So basically, I have been running off AUX heat exclusively. That combined with how cold it has been may very well explain the large spike in usage. I called a tech to come look at it. I will update and close this question once it has been verified.
UPDATE 12/10/2018 It has been a while so I thought I would share with everyone what the real issue was. After a few visits, it was finally discovered that my heat coils were stuck on. Even with the thermostat off, they were getting constant power. You could actually feel the heat radiating from the floor above the coils (they're in a crawl space). I'm lucky they found it, otherwise I could've had a fire on my hands. So yes, in essence, my AUX heat was running 24/7 for what was likely a month or two. CRAZY!
31
  • 4
    make sure that someone is not stealing power from you
    – jsotola
    Feb 27, 2018 at 21:17
  • 5
    Is your new housemate home during the day? they could be keeping your thermostat from going into away mode, they may also be turning it up too.
    – Jon
    Feb 27, 2018 at 21:57
    You can view your thermostat usage history here: home.nest.com/thermostat the website shows when weather or user adjustments account for higher or lower usage.
    – Jon
    Feb 27, 2018 at 21:58
  • 7
    First thing to do is to make sure your electric meter readings actually match the numbers on the bill. Second thing to do is to shut off all lights, space heaters, etc, turn furnaces off, etc, and then check to see how fast the meter is spinning. Then flip stuff on a few pieces at a time and see if there's a sudden jump.
    – Hot Licks
    Feb 28, 2018 at 3:17
  • 12
    >3000kWh used in Jan alone, so >100kWh per day? That's an average of over 4kW, non-stop. You'd think that would be detectable by looking for the thing that's glowing red hot.
    – Nye
    Feb 28, 2018 at 16:50
13 Answers 13
25
Since you say your backup heat is electric, I'd say that's what is using all the power. It could be that the weather is unseasonably cold and that the backup emergency heat is kicking in often.
Your Nest Thermostat could be switching to AUX heat more often than your old thermostat would have.
Since you say your nest thermostat is new (last summer), It is likely that it is responsible for kicking on the aux (emergency) electric heat more often than your old thermostat. There are settings to change how often this happens described below.
Your Nest thermostat may calling for aux heat more often than your old one would have. This can be configured with Heat Pump Balance which you might try changing to Max Savings or balanced. Note that the link below states that Max Comfort, the most expensive option, is selected by default. This is probably the issue. If changing this doesn't help, then I'd call an HVAC specialist.
Because auxiliary heat is so expensive, running the heat pump longer is still cheaper than using AUX heat. Heat Pump Balance automatically turns the heat on early to reduce AUX heat use as much as possible and get to your target temperature on time. It can turn on the heat up to 5 hours before a scheduled temperature if necessary. So if your schedule says 70ºF/20ºC at 7pm, Heat Pump Balance can use Early-On technology to start heating as early as 2pm.
Heat Pump Balance gives you four options to choose from:
  • Max Savings - This is the best setting for saving energy. In Max Savings mode, the Nest thermostat gives the heat pump more time to get to your target temperature before turning on AUX and sets a lower AUX lockout temp.
  • Balanced - This setting will give the heat pump more time to work, but will still turn AUX on quickly if it looks like it won't get you to your target temperature on time. Balanced has an AUX lockout temp somewhere between Max Comfort and Max Savings.
  • Max Comfort - When you choose Max Comfort, the Nest thermostat will make sure you'll get to the temperature you want, even if it means using auxiliary heat. Max Comfort is the default setting for Heat Pump Balance and generally gives you a higher AUX lockout temp.
  • Off - You can also turn Heat Pump Balance off entirely and adjust your AUX lockout temperature yourself. The AUX lockout temperature can be changed in SETTINGS > EQUIPMENT > HEAT PUMP.
There might be something wrong with your heat pump.
It could also be that there is something wrong with your heat pump. IE, it is running and using some energy but not generating any heat. Eventually, this will lead to the thermostat switching on the emergency electric heat and that will use even more power. Call an hvac specialist and have it inspected.
14
    @hack3rfx emergency and Aux heat are the same. If everything is electric, AUX heat is going to be very expensive
    – Jon
    Feb 27, 2018 at 21:54
  • 10
    That is probably my issue right there then. My thermostat is almost always on AUX. So would the best course of action be to have my Heat Pump checked and replaced if needed?
    – hack3rfx
    Feb 27, 2018 at 21:55
  • 4
    @hack3rfx Yes, have the heat pump checked
    – Jon
    Feb 27, 2018 at 22:01
  • 5
    @hack3rfx It could be that the nest was installed incorrectly. An HVAC specialist would be able to diagnose that. I could imagine an issue where the heatpump is never being used because it was connected incorrectly and it is always falling back to aux heat.
    – Jon
    Feb 28, 2018 at 16:26
    @DoktorJ Yes, I had intended on doing so. Many of the suggestions are going to be a waiting game, as well as trial and error. So it may be a bit before I determine the resolution. It's unfortunate I have to pick one answer though because they are all helpful and well thought out. Most likely all items contribute to some degree making them all correct in some way.
    – hack3rfx
    Mar 1, 2018 at 21:27
23
Do you have average temperature data for your area, so you can verify that it hasn't been "that cold". You didn't purchase any new electronics such as bitcoin miners with the latest craze did you? Have any close neighbors?
Cheapest thing if you have no electrical test equipment: go to the meter, on a lot of them you can see the least significant digit moving. Get a stop watch and time how long it takes to move 1 digit or however many you can easily decipher. Go to your circuit breaker and switch off one circuit at a time, starting with the biggest appliances. Go back to the meter and retest the time it takes to move however many digits. Turn the circuit back on and turn another off, repeat for all the major appliances and see which is drawing the most power.
I would suspect (assuming you turn off your HVAC most of the day): water heater top of the list, HVAC second. Dishwasher, stove, oven, microwave, also pull large amounts of energy but don't tend to be continuous and unnoticed.
  • I updated the original post showing the averages for my neighborhood. I also haven't made any big (electronic) purchases lately. As far as my neighbors go, it's highly unlikely they have purchased anything large as one of them is now a vacant house, and the others are more elderly residents. Now, this probably isn't relevant as my town has a population of ~3k and it's most likely considered one neighborhood, or it's likely very few at least.
    – hack3rfx
    Feb 27, 2018 at 22:04
  • 4
    There is a catch: if the main contributor is intermittent, there is a significant chance that it's off at the time of the measurement. The only chance to catch it would be to wait for it to be turned on.
    – clabacchio
    Feb 28, 2018 at 13:38
  • I would add the fridge to your list.
    – yo'
    Feb 28, 2018 at 17:57
  • 4
    @yo' Fridges are typically on a standard 15A receptacle, which would cap the usage at about 1300 kWh per month - the OP saw an increase of about double that over several months, reducing the likelihood that this is a single 120V device causing the increase.
    – mmathis
    Feb 28, 2018 at 20:50
  • Nah, with electric aux heat HVAC is definitely top of the list. Do the math - even adding an extra 20 minute hot shower every day can't burn the delta kWh OP is showing.
    – J...
    Mar 1, 2018 at 16:55
15
Mid-December through January were brutal in the midwest. Most days and nearly every night were below 10F.
Normal heat pumps cannot work at such low temperatures.
The heat pump was failing over to "emergency heat"
This is just a big bank of electrical resistors. I have seen installations where these resistors were on dual 70A breakers and ran well over 24kw - at common electric prices, that's $3/hour.
This wasn't your problem. But watch out for emergency heat incorrectly configured as "auxiliary heat" on the thermostat. The 'stat will call for that whenever it needs to speed up house heating a little bit, e.g. When warming it for your arrival back home. It presumes main and aux heat cost about the same or that you don't care. However the 'stat has no idea when the heat pump is too cold to work. The heat pump knows and it should call for emerency heat only when it cannot work IMO.
    Re: "only when it cannot work", the heat pump may "work" even at very low temperatures, but its efficiency drops off to the point where it takes the same amount of energy to pump the heat as the amount of heat it moves, making it no better and eventually worse than simply dumping energy through resistors. Feb 28, 2018 at 1:28
    Actually, this winter was pretty mild in southern Minnesota.
    – Hot Licks
    Feb 28, 2018 at 3:18
    That would certainly account for the extra 3.6kW average power he is consuming.
    – Trevor_G
    Feb 28, 2018 at 20:13
Disclaimer: I am located in central europe, so this may or may not apply for you.
In our region, typically every energy company and several environmental NGOs offer a service to borrow an energy meter for free or with a very small fee. Like this one: https://www.swm.de/privatkunden/kundenservice/energieberatung/strommesskoffer.html (it's in german, but just have a look at the pictures) Usual procedure is, you write to them and they give you date and time to pick up the equipment, and a week or two later you return the stuff.
There are meters for usual plugs, but there are also clamp-on-meters, which allow you to measure power consumption of directly wired appliances (e.g. if you suspect your ceiling light to run a server cluster up there).
IMHO this is the simplest, cheapest and most accurate way of having a power consumption survey in your home.
    I've not seen anything like that in the US. Interesting service, tho. The catch there is it looks like it only covers pluggable devices
    – Machavity
    Feb 28, 2018 at 13:39
    I know there are clamp power meters that work for non-pluggable devices. An example being this one: fluke.com/fluke/phen/clamp-meters/fluke-345.htm?pid=56070 but I can't name a specific power company wich lends out these. I would do the research around the companies I know, but it doesn't seem to be geographically applicable to OP. My first try would be to contact your local Greenpeace or any similar environmental organization. They tend to be pro-energy-saving and usually they know a lot about tricks like where to borrow a power meter. Feb 28, 2018 at 14:15
  • Since the Fluke 345 is about $3000 to purchase, there won't be abundant sources for lending it.
    – wallyk
    Mar 3, 2018 at 17:32
  • Non-logging clamp meters can be had for <$50. Power quality analyzers, like the mentioned Fluke 345, measure things like harmonics, which is way overkill for this problem.
    – user71659
    Mar 3, 2018 at 17:39
In a LOT of cases I've seen like this, it's turns out a problem with your water heater, assuming that if you have electric heat, you likely have an electric water heater. If the element is damaged, it leaks current into the water and immediately to ground, but because it's a high resistance ground fault, the breaker never trips. The fault in the element decreases the efficiency, so it almost never shuts off as it struggles to keep up with your hot water demand. You may not notice it in the hot water though, just in the high power consumption. Have an electrician check it for you.
    This is al ittle bit confusing because theoretically, the electricity leaking through the water should also produce heat.
    – user253751
    Feb 28, 2018 at 0:26
    @immibis electric current through water does consume energy, but that energy is used to convert water into hydrogen and oxygen gas through a process called electrolysis. You might find it interesting that electrolysis actually feeds on heat energy. In this way thermal energy is used for part of the electrolysis energy requirement, and thus at high water temperatures, a current leak actually COOLS the water, requiring the appliance to compensate. How much it cools or how much gas is produced requires calculations beyond me but thermodynamically speaking, electrolysis is counterintuitive.
    – Nathan
    Feb 28, 2018 at 7:13
    Do electric hot water heaters really not have GFCI?
    – Samuel
    Feb 28, 2018 at 9:23
    @Samuel I've not seen any, no. But you could buy a GFCI breaker for the panel (the amps needed require a dedicated circuit)
    – Machavity
    Feb 28, 2018 at 13:41
    No, GFCIs are not used on electric water heaters.
    – JRaef
    Feb 28, 2018 at 23:12
When heating a house, you don't pay directly for the temperature inside the house. You pay for the heat that gets away from your house. Dialing the thermostat down works because smaller temperature difference means slower heat transfer. On the other hand, increasing insulation gets higher temperatures at same cost.
If that new person enjoys fresh air and is keeping a window cracked open, or doesn't understand how thermostat works and instead of dialing it down opens the window, the thermostat will try to maintain the temp and this process can burn absurd amount of energy, as you're basically trying to heat up the world outside through the open window. I suspect the new person here, but damaged/removed insulation will yield same reason - when the heat is escaping, the thermostat will run heaters 24/7.
You should look for heat escape routes.
Then just look at your meter. The old ones have a spinning wheel, and the new ones have a blinking light. The faster it goes, the higher the energy consumption. For rough estimation, just looking at it helps, if you want exact numbers then you start counting - factor should be written on the meter, eg mine says "6400 pulses per kWh". However, I believe that this is a dead end. If you haven't brought any new appliances into the house, the problem is most likely an old appliance that now works much more than it did earlier.
What you want to monitor is appliance usage. It can be a simple sheet of paper when people log usage next to washing machine, etc. But that data is not easy to analyze without old data - just as you suspect more water heater use now, but you don't have historic water heater data. However, take a look at your old water bills - increase in water usage should be roughly proportional to water heater usage.
While the heat pump / HVAC is a very likely culprit and should be checked out first, it is possible that this is a combination of seasonal variations and the new roommate.
Looking at your graph, I'm guessing your roommate moved in sometime in November, as that's when your usage started exceeding that of your neighbors. Also, taking your neighbors' usage to be typical for your area and the season, you used an extra ~1300 kWh than they did in Jan (~800 kWh extra in Dec). Let's see if we can explain that away due to the roommate.
Water usage increases with the number of people in the house (roughly linear), so you should expect to use roughly twice as much (hot) water, meaning twice as much electricity to heat that water. Hard to pin down actual numbers without additional equipment or details, but hot water tends to be 10-15% of your utility usage:
source
This means you were using ~70-100 kWh per month to heat your water before the roommate. If your roommate likes long hot showers (and they very well might if they're not responsible for any of the electric bill!), though, that usage could more than double, so maybe it's an additional 150-200 kWh because of them. Any increase here should be readily apparent on your water bill, too.
Your roommate also does laundry and dishes, cooks, etc. Maybe you eat together, or combine dishes into a single run of the dishwasher, so this isn't exactly double your previous usage. Call it 1.5x though. Appliances tend to be another 10-15% of your electric bill (~70-100 kWh), so this could add an additional 35-50 kWh. That's 200-250 kWh extra total.
I assume your roommate has a computer, which is probably on all of the time. Even a low-powered one would consume ~70 kWh / month, but if they have a big machine and have it under load most of the time (maybe running Seti@Home, or another @Home project, maybe just gaming a lot at night, or maybe they're cryptomining), this could hit 500 kWh per month. That's 700-750 kWh extra total.
Add in some extra lights being on, maybe a TV in their room, device chargers, etc and that could be an additional 100 kWh a month or more. Total is now 800-850 kWh extra. That explains your December usage right there, though we're still a bit short on January usage. Maybe that is emergency heat, additional water heater losses due to extreme cold, etc, or it could be that our estimates were off.
As I said, this is not necessarily "normal" usage, but that it could be explained by non-broken things.
You, and all answers, seem to focus on the fairly obvious high energy consumer - water heater.
You mentioned that you recently got a lodger in your spare room. How well do you know what they do in their room? A colleague of mine recently discussed how his energy bill tripled from one month to the next - all thanks to an average-sized bitcoin mining rig. These are (usually) very specialised computers that are very fast and very powerful - and as a result use a lot of energy. He calculated his actual usage increased by roughly 1,000 kWh per month.
I'm not necessarily suggesting that this is what is going on, but it's worth checking.
  • I'm a developer and the only tech savvy person in the house. We don't do crypto currency at all. As far as what he does in his room, its mostly his tv and a playstation. No computer or anything.
    – hack3rfx
    Mar 1, 2018 at 1:07
You mention that your roomer has a TV and a game console. Large format LED/LCD flat screen TVs, despite the sales hype about being "energy efficient" are actually consuming a LOT of power. I have a 45" LED "Eco" model, it consumes 1.5kW (1500W) when it's on. That's like running a hair drier non-stop, or three 500W flood lights. Then even when it is off it is still consuming 50W continuously (hot standby mode). On top of that, a lot of gamers will pause a game so as to not lose their progress, then just get up and walk away, leaving the TV on 24/7. When my gamer son moved out, my power bill dropped by 50%!
  • 5
    What the hell kind of TV do you have? I picked up a cheap 60" Sony TV the other day, its rated maximum is 162W (and then you can tweak various settings to lower its power consumption). I could literally put nine of them in a 3x3 array for a 180" display, and still be using less power than you (though the display electronics to split the image across the nine screens might tip me a little past the 1500W mark)...
    – Doktor J
    Mar 1, 2018 at 21:21
You can tell relative power usage of a circuit by the temperature of the circuit breaker protecting it. Feel them and see if any are noticeably warm. You could also use an ir thermometer to check them more accurately.
If you suspect a particular appliance that plugs into the wall, I suggest using a Kill-a-Watt. It can measure instantaneous power draw as well as aggregate energy usage. It's pretty cheap, less than $30. Since you say your house is entirely electric, I imagine your water heater runs off electricity, but it may be wired directly without a plug.
There's another device on the market called Sense (http://sense.com) that works for all electricity usage at your home since it measures right at your breaker box. The product claims to tell you what appliances (based on the way they draw power) are on and when they are on down to the second. I've been interested, but it is $299 at the time of this writing, but I would think that is the ultimate, if pricey solution.
You might be interested in buying an Efergy Elite 4.0 Wireless Electricity Monitor. They cost about $100. I used mine for about three years until I had measured and recorded the KWH on most of the circuits in the house. It helped me to clearly understand that the main KWH users were heat, AC, and hot water heater. It led me to upgrade our AC/heater (Split Unit), add attic insulation, install an attic fan, insulate attic stairs, and other things and was able to prove it was saving money with before and after KWH consumption history. You use it at the circuit breaker panel; but, you have to be comfortable taking the cover off and connecting the meter clamp over the internal wires. It has a sending unit that you mount beside the panel, and a receiving unit you can place where you want. It also keeps daily KWH usage for about a week. I kept records in an Excel spreadsheet over a few weeks per circuit. Haven't used it in a couple of years now, but will if I start suspecting unusual usage. Oh, one more thing, it can measure 240v as well as 120v circuits.
-1
If you have an idea of what appliance might be causing the issue, you can use a device called kill-a-watt to measure the power draw.
amazon link
    That's assuming it is fed by a standard power cable; which most devices with really high draw wouldn't be able to run off of. If you suspect it's a device plugged into a normal socket, then this might work. In general, you'd expect really high power draw to come from things like heat pumps, electric heaters and hot water tanks; which in general don't use a standard 120 V socket.
    – JMac
    Feb 28, 2018 at 20:18