7

NEC rules sometimes refer to "the yoke".

For example: 1999 NEC § 210-4(b):

Dwelling Units. In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.

What is meant by the term 'Yoke' as used in the NEC?

1
  • 2
    You should really be using the modern NEC when dealing with multi-wire branch circuits. Not least it requires common maintenance shutoff on every single MWBC regardless. It also requires pigtailing of neutrals. Feb 17, 2018 at 8:30

1 Answer 1

8

The 'Yoke' is the structural frame of a receptacle or switch: yoke

It is often metal, with holes for two captive mounting screws, and should almost certainly be grounded if a grounding conductor is present.

Examples:

  • A light switch in a single-gang junction box has a single yoke.
  • Receptacles (in North America) are often manufactured in a pair of two outlets on a single 'yoke', which can be installed into one single-gang junction box.
1
  • I believe the yoke pictured is for a (normal, dual) NEMA 5-15 receptacle. It is "upside down" if you're used to receptacles being installed "like faces" in a home setting. Right side up if you install receptacles the "safer modern commercial" way. The two sets of contacts are what mate with the grounding pin on a nema 5-15 plug. That's some good connectivity between them and the ground screw isn't it? Aug 19, 2020 at 4:45

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.