4

With the 'Internet of Things' becoming more and more popular there's a myriad of 'smart' switches, bulbs, sockets and fittings that can be controlled over RF or Wifi.

With some of these solutions (Phillips Hue etc) the on/off switching takes place within the device itself, and ideally to avoid a situation where the fitting is switched off at the wall it would be best to remove the wall switch all together and leave all the control down to the various apps / remotes switches etc.

Which leaves me wondering -

1) Are there any regulations or best practises in the UK that require providing isolation to light fittings, other than at the distribution board for changing bulbs / maintenance etc?

2) If yes, can this isolation be provided by another 'smart' device with no physical switch other than an internal relay?

Disclaimer: I'm not an electrician, nor do I intend to make any changes. This is a theoretical question.

Thanks

7
  • Even if not required, physical switches are a very good idea. If you ever change out the smart bulbs for dumb ones (for whatever reason), you'll want to be able to turn off the lights.
    – mmathis
    Jan 14, 2018 at 2:02
  • Changing bulbs with the power still on isn't particularly dangerous. And even without switches, it's still possible to isolate them at the distribution box if required.
    – marrold
    Jan 14, 2018 at 2:12
  • you really want to have to run to the breaker box to turn out the lights before bed? And maybe UK wiring is different, but in the US at least, each light fixture is not on its own circuit.
    – mmathis
    Jan 14, 2018 at 4:48
  • Rather get switch guard locks these let you keep people from turning the switches off but they keep the switches where it needs to be.
    – Dan D.
    Jan 14, 2018 at 14:06
  • 1
    @marrold I live overseas now but I'll make reference to the last version of the wiring regulations I have available to me and give you a definitive answer. There are a lot of opinions in the comments above that don't directly answer the question.
    – Sam_Butler
    Jan 15, 2018 at 18:29

1 Answer 1

2

No precise regulation for a light switch

Except in the case of electric discharge lighting, there is no precise regulation that says you must place a switch, mechanical or otherwise, in or near a light, but in practice it would be unusual not to, and safer, more convenient, and more appropriate to the purpose of the device if you can operate a mechanical switch for that circuit or part thereof, rather than a circuit breaker.

Regulatory definitions and requirements

From BS7671:2008 incorporating Amendment No 1: 2011 (Requirements for Electrical Installations, IET Wiring Regulations, Seventeenth Edition)

Isolation. A function intended to cut off for reasons of safety the supply from all, or a discrete section, of the installation by separating the installation or section from every source of electrical energy.

Reg. 530.3:

Equipment shall be selected and installed to provide for the safety and proper functioning for the intended use of the installation. Equipment installed shall be appropriate to the external influences foreseen.

Reg. 537.5.2.3:

Off-load isolators (disconnectors), fuses and links shall not be used for functional switching.

Table 53.4 - Guidance on the selection of protective, isolation and switching devices:

This table shows that a circuit-breaker or RCD may be used for both isolation and functional switching.

Reg. 537.5.1.1:

A functional switching device hall be provided for each part of a circuit which may require to be controlled independently of other parts of the installation.

Reg. 537.5.1.3:

In general, all current-using equipment requiring control shall be controlled by an appropriate functional switching device.

A single functional switching device may control two or more items of equipment intended to operate simultaneously.

Reg. 537.5.2.2:

Functional switching devices may control the current without necessarily opening the corresponding poles.

NOTE 1: Semiconductor switching devices are examples of devices cable of interrupting the current in the circuit but not opening the corresponding poles.


Conclusion

Smart light bulbs, remotely controlled, are only switched after the fixed wiring and after a DC transformer. Therefore they fall outside the scope of functional switching within the meaning of the regulations.

In practice, what this means is that the light fitting would still be live when you remove a bulb, unless switched or isolated within the fixed wiring. Normally, this would be achieved by means of a light switch, but the regulations provide that a circuit breaker (not a fuse) can be used for this purpose.

Smart switches, inserted into the fixed wiring but electronically controlled, fall within the scope of the note to reg. 537.5.2.2 in that they do functionally switch the light fitting(s) such that in the off state, the lamp socket would not be live for the removal and replacement of a light bulb.

Smart bulb controllers that look like mechanical or electronic light switches but are not connected to the fixed wiring, are increasingly common, and aesthetically and functionally speaking it is not necessary to install a mechanical or even an electronic light switch beside such a controller. In the long-term however, should you wish to replace smart bulbs with non-smart bulbs, even on a temporary basis, it would be inconvenient at best to have to switch them off at the consumer unit.

My recommendation based on the above, where smart bulb controllers are installed, would be to install them over or beside a blanked switch box containing a link (with screw terminal blocks, for example) in which a switch could be installed. Alternatively, if non-routine switching within the room is desired, but accidental local switching-off is to be prevented, install the controller beside a secret key switch such as those in MK's Grid Plus range:

20 AMP SP TWO-WAY SECRET KEY SWITCH

2
  • 1
    Thanks for spending the time answering the question in detail. One query, you state that Smart light bulbs only exist after a DC transformer , however there are plenty with a built in transformer with a B22, E27 and GU10 fittings. Does the same apply?
    – marrold
    Jan 15, 2018 at 21:53
  • You're welcome. My point about a DC transformer is the same - the bulbs contain a transformer, after which part of the circuitry is switched to turn on/off the LED(s) contained within the bulb. If you take the bulb out of the socket, the socket is still live at mains voltage. The bulb is also still 'on' because some of the circuitry is required to maintain the radio for smart control, be it wifi, zigbee, zwave or another system.
    – Sam_Butler
    Jan 17, 2018 at 0:16

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.