-2
I habe done some renovations in my bedroom/bathroom and while doing so I had to remove the 4 gang box for the lights in my bathroom. Now I'm in the process of hooking the switches back up to the power and thought I got it done but I was wrong. So I have 4 switches;
  1. Main lights- above bathroom mirror
  2. Shower light
  3. Bathtub light
  4. Heat lamps
Each switch should work individually and the heat lamps do I believe I hooked that switch correctly. Problem is switches 2 and 3 only work if switch 1 is on. Now they only thing I was confused with were the 3 sets of wires coming up through the floor from the breaker. I know one is for the heat lamps leaving 2. I thought the other 2 sets were for bringing the power up and the other is to continue the power back somewhere else since the 3rd set of wires are not hot when all breakers are on. So what I did was connected the 3rd set with the 2nd set so essentially it would continue the circuit to wherever it continues to. Obviously I'm doing it all wrong can someone please assist me heat lamps and shower light  4 switches far left is heat lamp switch next is tub,then shower, and main light is switch on far right and below are the 3 sets wire and noticeable the 2 sets that are in question main mirror lights and to the right is the tub light enter image description here
18
    You may find this answer helpful. The trick is colored tape. Jan 12, 2018 at 18:10
  • @Harper the problem is not figuring out what wire power which light it's the wires beneath the box coming from the breaker. 2 out of the 3 carry power to the gang box while the 3rd does not. Initially I thought the 3rd wire was to carry the power back out the gang box and on to somewhere else that needed power. By thinking that I added that wire into my pigtails that were made when powering all switches
    – J.Monte
    Jan 12, 2018 at 18:46
  • If you follow the color code idea for the wiring that Harper linked to you will probably figure it out, I say this because 1 switch controlling the others means the common hot is wrong that's why when sw1 is on the others now have power. His explanation is easy to follow+
    Jan 12, 2018 at 19:26
  • I might get around to a better answer later, but generally speaking, none of the switches should feed into each other (unless you want to enforce a global on-off with subcomponent switches). It sounds like switches 2 and 3 are being fed from switch 1.
    – Hari
    Jan 12, 2018 at 19:53
  • Let me better explain and hopefully it will help give a better picture. The wire coming from the panel was connected with the other wire that I think goes on to power other outlets or lights as well as 3 pigtails, one for each of the 3 switches. (4th/last switch is wired for the Heat lamps and is working correctly). After connecting the 3 pigtails and the separate continuing wire to the panel wire with a wire nut I then proceeded to wire the 3 switches by plugging them into the bottom wire hole of the switches. I plugged all the wires going to the desired fixtures into the top hole of the
    – J.Monte
    Jan 12, 2018 at 21:41
There should be one cable that is the hot feed from the panel. All the others are switch legs to the equipment.
It sounds like you somehow fed switches 2 and 3 through switch 1.
All of the switches should be fed with the same hot from the main panel cable. All of the neutrals should be tied together through to the equipment. Each switch leg would then go to each piece of equipment after its respective switch.
Good luck!
    – J.Monte
    Jan 12, 2018 at 21:52
  • Switches. All neutrals were connected already and wire nutted together as well as the ground wires were grounded as well. So essentially all I did was turn the hot black panel wire and turned it into 3 panel wires and connected the wires to the 3 switches. This is why I'm so confused on why this is happening and what I'm doing wrong
    – J.Monte
    Jan 12, 2018 at 21:53
    Well, depending on the rest of his wiring scheme, it's possible that two sets of cables come from the panel. In my house, all the lights are on an isolated circuit to prevent a receptacle/outlet from tripping a breaker and turning off the lights. If this is true, then the heat lamps might be on a different circuit due to their current requirements, especially since it all looks like 14/2 to me.
    – Hari
    Jan 13, 2018 at 22:29