I’m running 10-3 Romex for a 240v electric dryer in our garage. It would be very convenient to tap into one hot leg and add a 120v outlet for the washer (they will be stacked). Is this allowed per NEC code?

Also, can I add an additional 240v outlet to this circuit to future proof the garage for such things as a table saw or welder? Or does the dryer require a dedicated circuit with no other outlets?

  • 1
    No you can’t combine the washer and dryer circuits. You wouldn’t want to either, the washer is a large enough load that you couldn’t run the dryer at the same time. – Tyson Dec 25 '17 at 3:32
2

You can't tap a cable like that - NEC has a whole section called the "tap rules" which describe when you can do that, and this is not one of those times. Even if you could, it would be a lost cause: Since a washer must be provisioned for 20A, that plus the 30A dryer puts you at 50A, and you'd need to run the expensive 6/3 cable.

Here's what you can do:

Pull a 12/2 cable alongside the 10/3 cable

That may seem stupidly obvious, but for the cost of a 12/2 cable, you are done. It will take an additional breaker space.

Run 6/3 and install a subpanel

You can run 6/3 cable instead of 10/3, terminate at a small subpanel, then have a 2-pole 30A breaker for the dryer and a 1-pole 20A breaker for the washer. I believe the subpanel would need to be at least 50A.

Run 10/3 to a subpanel with a "generator" interlock

Use the interlock so you can only operate the 30A breaker for the dryer, OR, the 20A breaker for the washer. You would have to throw the breaker every time. Very tedious. This will get old fast.

Buy a washer-dryer set that's designed for that

Large housing complexes are typically out to minimize the utility work they must put in laundry rooms. Industry caters to them with washer-dryers designed to run together off a 30A/240V receptacle only. They are either sized correctly, or have logic to manage electricity usage so they can't overload the 30A circuit. They make combo units (washer + dryer in one unit) which tend to be tenant-tier cheap in their feature set... or they make matched set washers + dryers which can be deluxe, but expensive.

0

This would not be allowed for several reasons one being the dryer will be protected by a 30 amp breaker the other is that the last 2 code cycles require a 120 v 20 amp dedicated circuit for the laundry.

  • I believe there is no rule about adding additional 120v circuits to the dedicated laundry circuit as long as they are in the laundry room, is that correct? If so, would my garage be considered the laundry room and can the washer share the circuit with the other garage outlets? I have limited breaker box space and would rather not use one for a single 120v outlet to run the washer if I can avoid it. – gorms Dec 25 '17 at 17:09