0

Bootleg ground means a scenario equivalent to (deliberately) bridging the ground wire and the neutral wire.

How it was physically done (e.g. bridged screws on a receptacle, deliberately bridged wires in the wall without a junction box, or otherwise) is hard to find in a home one moves into. This DIY.SE post shows the dangers of bootleg ground: one fault can energize everything, including metal chassis. Does replacing the example’s regular receptacle with a GFCI receptacle alleviate the problem at all? This 05/30/2017, 09:39 Wikipedia entry implies it won’t, but doesn’t cite a source, so I’m not sure about its correctness.

This other DIY.SE post implies any GFCI with bootleg ground can’t be tripped by external testers but can be tripped by its own test button, but given that Wikipedia entry, I’m not sure which one is correct. If Wikipedia is correct, does that mean such GFCI can’t be tripped with either method?

I tested 2 GFCI receptacles and they’re on different circuits. I used the Amprobe INSP-3 wiring inspector circuit tester. One GFCI can be tripped by both its own test button and my circuit tester. The other can’t be tripped by either way. I measured .45 ohm ground impedance on the latter. Does that mean bootleg ground? This video says properly wired receptacles should have 1 ohm impedance. The video’s bootleg ground receptacle tested with .03 ohms impedance using the same tester. Amprobe throws a warning if it’s ≤.04 ohms.

How can I make such GFCI receptacle extend protection downstream and function properly without adversely affecting any other receptacles (on the same or different circuits), breakers, or main panel?

Is it as simple as disconnecting the GFCI's ground wire on the line side? Must I also disconnect the ground wire on the load side? Could this adversely affect bootleg-ground upstream receptacles?

Must I also disconnect all ground wires on the line and load sides of all downstream receptacles, too? Is it safe to leave said disconnected wires in the box or wall? Or, is the only solution to tear the walls apart?


Which does any GFCI disconnect upon tripping: ground, line hot, line neutral, load hot, load neutral? If tripping doesn’t disconnect ground, then wouldn’t a disconnected upstream neutral be dangerous if there's a load elsewhere on the circuit?

I’m in a guest house that has a (sub?)panel that likely sources from the old main house. The main house likely has bootleg ground receptacles and I don’t know what’s inside its panel other than it doesn’t have GFCI breakers.

The .45 ohms ground impedance was measured in the main house’s GFCI receptacle. The guest house has all non-GFCI breakers & non-GFCI receptacles, the latter of which measures .04-.07 ohms ground impedance. Are these bootleg ground? I see 3-conductor Romex when opening some of guest house's outlet covers but can’t search everything. I don’t know if guest house’s Romex is correctly wired or if it matters given main house’s condition.

Would installing GFCI breakers in the guest panel be safe or can the main house’s condition energize the guest panel?

If it’s safe, would these breakers protect everything downstream if some or all downstream receptacles or unmarked junctions have bootleg ground? Must I disconnect all downstream ground?

For the guest house, I have the same question if opting for a GFCI receptacle instead. What are the dangers of replacing a regular receptacle (that has 3-conductor Romex which might be compromised upstream with bootleg ground) with a GFCI receptacle in the middle of a circuit and connecting the GFCI receptacle’s ground?

3
  • Actually, bootlegging ground means deliberately connecting grounds to neutral because there's no ground in the cable and you want to pass inspection. See also NEMA 10. It does not apply to a case where somebody ran a drywall screw into a Romex cable and shorted neutral and ground, that is a wiring failure not a miswiring. There's a big difference, ask your claims adjustor. Dec 24, 2017 at 0:01
  • @Harper, I meant deliberately, but didn't think of drywall nails. When I mentioned "without a junction box", I meant that people may have been cheap and wired everything in a hole in the wall and put the drywall back up.
    – CodeBricks
    Dec 24, 2017 at 4:56
  • If both neutral and ground were available upstream and downstream, there would be no earthly reason for someone to want to short them together. Bootlegging is done because one is absent and is needed, e.g. NEMA 10, using ground for neutral in a 240V-only circuit, etc. Dec 24, 2017 at 5:44

3 Answers 3

4

If you don't trust a ground, don't connect to it - use GFCI instead.

If a GFCI won't trip with its own internal test button, it is duff. Into the trash it goes.

Here is how GFCIs and ground wires are supposed to relate to each other -- or to be more precise, how they are not.

enter image description here

To the left you see unprotected hot and neutral coming in, out the right you see protected hot and neutral, which I've recolored. Ground sails right by unconnected (normally). Obviously, if your ground is corrupt/defective, this is bad news indeed.

"Wait, all the GFCI's I've ever seen have a ground screw." No. That thing you call a GFCI is actually a GFCI+receptacle combination device. It provides a GFCI module, and also two sockets (wired past the GFCI). The GFCI can't use ground. Look at a GFCI breaker, it doesn't even have access to ground. The ground is for the sockets. This means effectively, that ground screw is on the "protected" side of the GFCI.

So if the ground is bad, where should you cut the ground? Before it reaches any protected loads, and remember, the ground screw on a GFCI+receptacle combo serves the protected loads.

Should you do anything creative like tie the protected-side ground into protected-side neutral? No No No! This post of mine explains how that utterly defeats the GFCI protection. Wrap the ground wires with tape so they can't touch, and don't use them.

Detecting tied ground-neutral

If your panel is set up this way, the single easiest way to test your neutral-ground isolation is to disconnect your neutral-ground bond in your main service panel. Now the only thing connecting neutral and ground is that long path of dirt between your grounding electrode system and the pole transformer's. If you also unhook your grounding electrode, your house's internal grounds should be fully isolated from neutral, and should megger out at a couple megaohms. (Don't megger things in residences though, it could fry electronics).

Or test circuit by circuit. It's a simple thing, on any given circuit there should be 0.000 amps of current flow on the ground wire. Nothing is supposed to use ground but test equipment. Now, if neutral and ground are tied together, current follows all paths in proportion to their conductance (1/resistance) so a significant fraction of current will take ground instead of neutral (assuming there is a load). Obviously a GFCI will detect the shortfall, but a clamp meter will detect the ground current directly.


I don't agree with that video's claim of nearly 1 ohm between neutral and ground. Copper wires have much better conductivity than that unless he has many hundreds of feet of wire between his lab and his main panel. There may be something peculiar going on in his test lab, or he is misunderstanding or misusing the equipment. You shouldn't have 1 ohm neutral-ground, that would limit dead-short current to 120A, which would not flow enough current to safely magnetic-trip a breaker.

In any case, a clamp ammeter around the N-G bond (or a circuit's ground wire) would soon show if any AC current was flowing.

2
  • I appended to OP below line. In short: I’m in a guest house. Measured GFCIs were in main house. Guest has its own (sub?)panel & likely sources from older main house, which likely has bootlegged receptacles. Don’t know what’s in main house’s panels other than it’s not GFCI breakers. Though I see 3-conductor Romex in some guest receptacles (so far, didn’t check everything), I don’t know if they’re legit, because .04 ohms impedance. Is it safe to only replace guest’s breakers with GFCI? Or only replace a mid-circuit receptacle with GFCI and connect ground wire, which might already be bootlegged?
    – CodeBricks
    Dec 24, 2017 at 4:53
  • 1
    @CodeBricks Oh! It's a subpanel. Well that makes it easier and/or harder depending on if it's an old grandfathered panel without separate neutral/ground. I think you are relying too much on magic readouts from that tester and not enough on direct inspection and simpler measurements. If you can't test for current flow on the master ground-neutral bond, then check for current flow on each circuit's ground. There should always be 0.000 none, except when you are sticking a tester in the socket. Dec 24, 2017 at 5:41
2

What are the dangers of a GFCI receptacle downstream of a bootleg ground receptacle?

The primary danger is that future users may assume they have a proper grounding conductor, when they actually do not. Of course there is also the obvious problem of having a receptacle without a grounding conductor.

how can I make this GFCI receptacle function properly without dangerously affecting any other receptacles...?

It will function properly and will not dangerously affect any other receptacles, with or without a proper grounding conductor (except for the fact that it has none).

Can I fix it at the point of the GFCI receptacle such that all receptacles downstream from it are protected?

If all downstream receptacles are wired from the "Load" side of the GFI, they will be GFI protected. They still will not have the safety protection provided by the grounding conductor.

You should remove the receptacle with the "bootleg ground" and replace it with a GFI receptacle, abandoning the "bootleg ground". Then feed all downstream receptacles (these do not need to be GFI receptacles) from the "load" side of that first one. All will be GFI protected. All must be marked "No Grounding Conductor".

7
  • While the GFCI receptacle is connected to false ground by being directly on the load side of the bootleg ground receptacle or indirectly further downstream, will the GFCI receptacle inherit the same problems as the bootleg-ground receptacle (energizing every ground in your house including the service panel itself [& device chassis])? Also will this GFCI receptacle never trip? This says it won’t get tripped by external testers, but I’ve a GFCI receptacle that won’t trip even with its own test button
    – CodeBricks
    Dec 23, 2017 at 3:55
  • Wait, I assumed the OP was talking about a bootlegged grounding conductor, not a bootlegged grounded conductor, i.e. neutral. No way should any receptacle (or any other device) be operated without a proper grounded conductor. Dec 23, 2017 at 4:59
  • What is a "grounding conductor"? Sounds a lot like their goofy name for a neutral. Dec 23, 2017 at 12:05
  • 1
    @Harper - This is how I was taught. A grounded conductor (neutral or phase leg) normally carries current. A grounding conductor (the ground wire green or bare) normally does not carry current. GFCI's function use that principle. In theory a correctly installed system you should not have any current running through the grounded conductor and all current should be returning through the neutral and other conductors. PS - Grounded phase legs are an old industrial system no longer being installed but doesn't mean you won't run into one every once in a while. Dec 23, 2017 at 17:03
  • 1
    It just says NEC prohibits an isolated ground rod as the only means of equipment grounding, that's because the ground should return to the source. That's why your grounding conductors are connected to a ground rod and are bonded to the neutral at the main distribution panel. Thanks Three Phase Eel. Dec 24, 2017 at 1:31
1

Beware of the dreaded reverse polarity bootleg ground!

Bootleg grounds by themselves are only a minor hazard if there is a GFCI downstream of them -- they can simply be left unconnected at the GFCI location if this is a concern in an existing-construction situation like the OP.

However, if there is a reversal of polarity (hot/neutral) anywhere upstream of the bootleg point, then you get into a situation called a "reverse polarity bootleg ground" that is an extreme shock hazard. In short, devices still see 120V H-N, but that's because H is the 0V point and N is at 120V. The bootleg ground subsequently puts G at 120V (!!!!), and since GFCIs only disconnect load-side H and N (not G), not even a GFCI can save you from getting zapped by the reverse polarity bootleg ground!

Canonically testing for it requires some way to get back to a known-good bond to the grounding system, but a quick test can be done with a non-contact voltage tester (volt-alert, volt-stick) as having 120V on G will make the ground strap of the receptacle "hot" to the tester. Normally, a non-contact tester will only trigger if you put the tip in the hot slot on a receptacle.

Subpanels are a different story

Of course, this is all about branch circuit grounding. A 3-wire subpanel, especially to a detached structure, is a different story -- if you swapped neutral with one hot on that, then you'd have half your receptacles delivering 240V, which'd be quite a noticeable issue, in addition to the panelboard cabinet being live, and your watthour meter spinning off into oblivion due to parasitic current flow from the detached structure's electrode to the utility earth electrode via the ground.

So, I'd consider the hazard somewhat lower for a subpanel provided the feeder itself is properly run. If you can get the owners to replace the feeder with a proper 4-wire feeder and pull the subpanel bonding jumper though, I'd do that anyway -- that way, everything's all up to modern Code as far as the feeder goes.