Honeywell T8411R Thermostat

This is the wiring of my Honeywell T8411R. I noticed my room was not warming up. I moved the switch to Em.Heat and still no warm air blowing in ducts. I would like to test if my thermostat is sending signals. How do I do that with the given wiring configuration? My fan is working. How do I first test with Emergency Heat? I have split system.

  • Do you have gas or electric emergency heat? – ThreePhaseEel Dec 10 '17 at 21:42
1

With that thermostat it would be easier to tell if the air handler and heat pump are working rather than the thermostat. The thermostat doesn’t send a signal it closes switches just like a few automatic light switches. So you just need to see if the switches are closing. With that thermostat it may be a little difficult especially if it is not battery powered. To test the air handler connect a jumper wire to the R terminal and to the G terminal. That will turn on the fan. To test the emergency heat connect a second jumper from R to W2. This would turn on the emergency heat. Remove the jumper from W2 and place it on Y/W1 to turn on the compressor. Placing a third jumper between R and B will energize the reversing valve and cycle between heat and coil. Whatever you do, do notjump anything to C or at best you will blow a fuse and at worst let the smoke out of several components. If all that works but does not work after reconnecting the thermostat it is most likely a thermostat problem. If the thermostat is battery powered you could use an ohm meter to tell is each switch is closing or not. Each one of those pins on the bottom go to a terminal. Find which terminal they go to using an ohm meter. Then insert test leads into the corresponding holes in the thermostat and do the same as above except instead of different pieces turning on your ohm meter will go from OL to 0

0

Well the thermostat has to be in place to do the testing. The testing will be done at the furnace or air handler. If and when you have a heat pump it is more difficult because you have to activate the reversing valve in the heat mode and different systems do it differently. It sounds like you are describing a heat pump system. The yellow will be energized to suck the compressor relay together. The green will be energized to start the indoor blower. And either the orange or brown with either be on or off depending on the system to put the reversing valve in the right position.
With a fossil fuel furnace, it is far easier. With a call for heat the white will be energized. The IFC (integrated furnace controller) takes care of the rest.

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.