1

I am installing a three wire 16v transformer. My 1960 20 circuit breaker box has only two connections, hot & ground.

What to do with white neutral wire?

2

Some things don't make sense here. Standard low voltage transformers should have a hot, a neutral and a ground wire. They are single phase and should be installed into the side of a standard junction box through a 1/2" knockout. Then you just match the wires to the circuit wires. The low voltage connections are then on the outside of the box.

Low voltage transformers aren't normally attached to the main circuit panel since their wires are usually too short to reach the connections. There is nothing in the Code saying you can't, you might just have to extend the wires.

Even in 1960's, houses in the US were built with split phase three wire services. The main panel would have two hot legs attached to the breaker bus bars a neutral and a ground bar. At the main panel the neutral and ground wires can be mixed on the same bars. If you choose to attach it to the main panel, the neutral and ground wires should be attached to one of those bars.

The National Electrical Code prohibits the use of course-thread self tapping screws for ground connections. The threads have to be fine enough to engage a minimum of 2 threads in the material of the enclosure. See 2017 NEC 250.8(A)(6).

Good Luck!

1

Could you post a picture of the inside of your breaker box? We can point out what is what for you.

There should definitely be a neutral bus bar in there (or a bunch of neutrals wire nutted together at the very least), so you're probably mistaking that with the ground.

Your problem will be if there is no easily accessible ground available. If that is your problem, then let us know and we'll tell you what to do.

Also, don't put the doorbell transformer inside the breaker box. The low voltage side shouldn't share the same space as the high voltage side, so mount it on the outside of the breaker box or on the side of a electrical box.

  • 4
    Fyi, a self taping screw is not a legal grounding method. We see it all the time but not code unless it is a machine screw so not less than 2 threads are in contact. NEC 250.8, there are machine screws that are thread forming (32 threads per inch) these are legal. – Ed Beal Nov 29 '17 at 20:05
  • @EdBeal Thanks Ed! I removed that part from my answer. – Dotes Nov 30 '17 at 1:34