I need to run power to my loafing shed for lights, fans and blowers for show livestock. The blowers pull almost 20 amps each so here is my plan.

  1. Underground service using 4 awg thwn in conduit. 130 ft run.

  2. 60 amp breaker in main panel

  3. Outdoor Sub panel in shed. The shed is covered on 3 sides and front is open.

  4. 2 ground rods at subpanel. May have to install horizontally due to rock in ground

  5. 3 circuits coming off subpanel. 2 dedicated for the blowers. 3rd will be for lights, fans and stock tank heater. All outlets will be 20 amp on gfci.

  6. Obviously stock tank heater will be close to water so I will use liquid tite conduit there.

My questions are

Do I need a gfci breaker for the 60 in the main panel? Will 4 awg wire fit in a 60 amp breaker? Is 4 awg large enough? Can I use aluminum? Is 1" conduit large enough for 3 4 awg wires. I will not need 240 so only three wires

I have found hundreds of threads on how to run power to a shed but this is different since it's not completely protected from the weather.

Thank you


Thank you for your help. A couple of things I left off. One is I'm out of city limits and no imspection required, but obviously want to do this safely. Two is the structure is wood frame with metal siding/roof.

After some more research and reading here, I've come to the conclusion of running 1 awg Al as my feeder. My current shop panel this will feed off of is wired up with 2 awg Al.

Another problem is getting the 1 awg Al hooked up to the 60 amp breaker. My plan is using one of the Polaris insulated connectors. Anything wrong with that? If I understand correctly I can connect my Al with Cu with no problem with corrosion.

If everything I run is 120V, will running 240V to this shed help anything?

I get the idea of using 240V for the blowers, but we take them on the road to shows and there are no 240 outlets available. I will have to buy two sets of blowers. One to use at home and one on the road.

As far as using 60 over 100, I don't know. Just have to pick something I guess and go with it. The 100 sounds like a good idea.

I did look at my neighbors setup today and his is very similar. I am concerned now because his subpanel is wired with 2 awg Al on a shorter run and he said the blowers will trip a breaker on startup during the winter. After the breaker is reset everything is fine. He is also using an extension cord off his panel. I run into the exact same problem currently when I use my metal chop saw. It trips on startup and works fine after reset. My idea is to wire up gfi's maybe using 10 awg off my panel.

I do believe the weak link will be one I cannot easily fix. My shop is about 150' from the meter. The electrician who wired it used 2 awg Al up to there. I found some 2-2-2-4 Al mobile home feeder at Lowe's today for $1.50/ft. I think I will use it ran in some conduit unless somebody tells me that is a bad idea.

Again thank you very much to everyone for your help with this.

He's tripping the 20 amp branch circuits.

I do have one more question. The scenario is my shop is concrete floor with metal framing and siding. Panel is mounted to wall via struts. #2 Al ground wire is ran from the meter to the panel. I don't believe they ran a separate ground rod to the panel. I already have a ground rod right outside the building where we had some lightning rods installed. Am i going to hurt anything by running a ground wire from the panel grounding bar to the ground rod? It's going to cost me a few dollars for 6' of Cooper wire to do it and next to zero effort.

Also was thinking about burying a ground rod in the trench for my water line and use it to ground the water tank (run the wire into the tank) where the heater will be locate. This is what the manufacturer of the heater recommends. Then tie it into the ground on the outlet box where the heater plugs in. Good idea? I assume it's impossible to have too many grounds?

11
  • 1
    Actually, can you run the blowers + heater on 240V? That'd help tremendously here...also, do you want/need convenience receptacles at the shed, or are you OK with just lighting and the fans/blowers? Aug 18, 2017 at 2:27
  • The exterior panel is fine they may require Myers hubs but if it dosent get wet they should not be required. No requirement for the 60a gfci. You will want the stock tank heater on a GFCI the ones we have are 120v and are. Corded but if hard wired liquid tight will work. If you do have to go horizontal you may want to think about a ground loop because livestock are much more sensitive to stray currents. Motor loads like fans can be a prime source of stray currents from my barn experience.
    – Ed Beal
    Aug 18, 2017 at 3:02
  • @Justin -- what's the rationale for the Polaris connector btw? Can I ask what make and model the 60A breaker in question is, even? Aug 19, 2017 at 3:41
  • 1
    Use the edit link underneath your post if you want to update it. Don't post updates as an answer. Please see the tour, How to Ask and How to Answer for more information.
    – Niall C.
    Aug 19, 2017 at 4:42
  • 1
    If you are going to use #1 aluminum then you can go up to a 100 amp breaker. Why do 60 when you can have 100? Wire will fit and you can run more equipment.
    – ArchonOSX
    Aug 20, 2017 at 0:04

1 Answer 1

4

Fatter is better

Upsizing your conduit now costs pennies compared to having to dig it up and replace it later, so I'd put the fattest Schedule 80 PVC you can in now -- at a bare minimum, I'd go with 2", with say 3" being an even better choice if possible. This will also make your pull job easier than if you used the smallest possible conduit -- it might even save you a call to the electrician and their truck o' tools!

Also, don't try to stuff a nasty ol' SE cable down that conduit -- you're using more fill than you need as SE cables are made with fatter ground wires than strictly necessary, and the jacket is simply going to hamper your pull, as well. It might mean you have to hit up the supply house or order in the appropriate XHHW-2 single conductors, but you'll be thanking yourself that you did when you are doing the pull!

4AWG Al will do the job, but you probably want fatter wire than that as well, or to go to 240V

While putting 60A through 4AWG Al XHHW-2 with 75°C terminations is within the NEC's ampacity limits, it does yield a 6.5% voltage drop, which is well in excess of the 3% limit recommended for feeders. Staying at 120V means you have to go up to a whopping 1AWG for aluminum conductors to get the voltage drop close to 3%; 240V gives a major advantage here, allowing you to run over the 4AWG with a voltage drop less than 2%.

Speaking of aluminum -- unless your AHJ is ridiculously fearful/uninformed and requires copper for everything, which I have heard of in some towns, modern aluminum is fine for a feeder -- breaker and panel lugs in loadcenters are all aluminum-rated these days, and the AA-8k series alloys used for aluminum building wire these days aren't nearly as ill-tempered as the old EC grade stuff. Still, it's essential that you torque the lugs to the breaker/loadcenter manufacturer's torque specification (an inch-pound torque wrench with a screwdriver bit adapter will do the job) in order to produce a long-lived connection as aluminum isn't as forgiving of overtorqued connections as copper is; never mind that the 2017 NEC requires the use of torque tools these days! (See 110.14(D) for details.)

Speaking of 240V...

240V to the shed is a better bet than 120V to the shed given the size of your feeder and your loads:

  • Your 20A 120V blower motors clock in at 1.5HP apiece -- motors this size should be able to be rewired for 240V, or at least available in 240V versions.
  • Modern LED drivers and fluorescent ballasts are available in 120-277V universal voltage options, so that takes care of your lighting
  • Fans are definitely available in 240V as well -- if nothing else, you can get condenser fan motors and use those

This leaves the stock tank heater and possible convenience receptacles as 120V loads; that, and any GFCI protection itself you want as two pole GFCIs require a line neutral as the electronics inside run on 120V. Given that, I'd run a neutral + 2 hots and ground, so that both 120 and 240V loads can be accommodated, while keeping the amount of 120V load down . More specifically, I'd go with 1800W max for the stock tank heater -- this leaves you with 15A on the other side for the convenience receptacle if you wish one, 20A for both blowers when wired for 240VAC, and another 5A@240VAC for the lights and fan, allowing us to get by on 40A total. Of course, if you're stuck with a 120V fan, that will increase things a bit unless you can get away with a smaller stock tank heater.

However, since you're stuck with 120VAC for the blowers, the best plan is to run 240VAC anyway as that gets you two opposite legs -- stick one blower on each leg, with the fan + lights + receptacle on one leg and the stock tank heater on the other. This again gets you down to 30/40A of 240VAC, which is a cakewalk for 1AWG aluminum and eminently possible on the 4AWG.

Livestock hate tingly electrical feelings

Livestock don't put up well with stray currents that us humans tend to shrug at -- their longer gait means that they get more step potential than us humans do, and they aren't as good about voicing their displeasure about the situation to the electrician either.

This means that your grounding system is rather critical. If I were you and I was building this barn from scratch, I'd use a full equipotential grid in the style of a swimming pool's, laid into the barn slab and exothermically welded to the slab reinforcing steel as well. Since that horse is likely out of the barn already though, I'd use an equipotential ring ground electrode consisting of a circumferential trench just outside the barn footings, dug to the footing depth, the water table, or bedrock, whichever comes first. Into this trench goes appropriate reinforcing steel as well as copper wire mesh (again, you can get this stuff for pool equipotential bonding) formed into a vertical I-shape and exothermically welded to the rebar. A 6 AWG bare copper "tail" is exothermically welded to the mesh near where the feeder enters, and concrete is poured around this all. The tail then serves as your grounding electrode conductor and attaches to the ground bar in the structure's subpanel; it doesn't need damage protection either provided it's run along the barn wall.

Needless to say, the feeder must have a separated equipment grounding conductor (I'd use the same 6AWG copper as was used for the "tail", pulled through the conduit with the rest of the wires), and the neutral/ground bond at the subpanel must get pulled, or else you'll find yourself in stray current HELL as the earth, your feeder EGC, and your feeder neutral all wind up in parallel if the subpanel is left bonded.

As to the stock tank? I'd run more of that 6AWG copper from either a bonding plate inside the stock tank (get a "Bondsafe 680" or equivalent from the nearest swimming pool people) if it's fiberglass/nonconductive or a solid connection (listed lug, exothermic weld) to the stock tank itself if it's metal to the outlet box for the stock tank heater, where we attach it to the ground wires there. Again, the basic idea here is to make it so everything's as close to the same potential as possible.

GFCI protection is better provided on individual branch circuits

Most smaller subpanels (100A and below) use a backfed main breaker architecture -- the main breaker is really a repurposed branch breaker. This is fine for ordinary breakers, but won't work with a GFCI in place of the submain -- trying to feed power into the LOAD end of a GFCI breaker is a good way to fry the GFCI's trip solenoid. As a result, it's better to put the GFCI protection, in branch breaker form, on the individual branch circuits that need it -- any convenience receptacles will need such protection, and it'd be wise to GFCI protect the stock tank heater as well. Putting the GFCI on the upstream end of a long feeder isn't wise either, because the leakage currents to ground on long feeders can be a bit on the significant side, contributing to nuisance tripping.

Last but not least -- the QO260 and HOM260 accept up to 2AWG wire -- so you can use a short length of 4AWG aluminum or copper as a pigtail between the breaker lugs and an AlxCu rated mechanical connector, such as the Polaris connectors you mention. Note that the Polaris connectors that accept 1AWG require pretty heavy torque for a connector, so you'll need a torque wrench capable of 180 inch-pounds or 15 foot-pounds to tighten them. The liquidtight conduit is fine for a hardwired stock tank heater, although I'd run a dedicated ground wire inside it even if it is LFMC, and a typical NEMA 3R is fine for the loadcenter box no matter where you put it (I'd be leery of using a NEMA 1 enclosure inside a three-sided shed though, as sideways rain is a thing where I live.)