I need to wire up my attached workshop, which is about 50' from the main panel. I don't want to make a bunch of homeruns and would rather install a workshop-specific panel for this task. I will be running the following:
- 5HP Planer - 30A 240V
- 5HP Shaper - 30A 240V
- 1HP Power feeder - 15A 240V
- 2x 1.5HP Shapers - 15A 240V
Down the line I will also be adding an air compressor and a dust collection system. Obviously I will not be running all of the equipment at once, but it's very likely that I might run my 5HP shaper, 1HP power feeder, and my dust collection system at the same time in the very near future.
Having said that, I'm trying to figure out how to make my life easiest. My main panel is located outside on the opposite side of the house, so the plan is to run in conduit down to my crawl space and then once inside, run through the joists without protection. Here are my questions:
- I will feed my subpanel with 4 wire cable. 2 hots, a neutral, and a ground. Right?
- In my subpanel, I will NOT bond my neutral and grounding blocks. Ground and neutral will be independent. Right?
- What size subpanel should I get for these needs? I was thinking a 60A. Right?
- What size wire? For 60A at that distance, my calculations say 6 gauge copper. Is that correct?
- I don't intend on placing a ground rod anywhere, as this subpanel is attached to my main structure (And the subpanel is inside, it'd be very difficult to drive a ground rod anywhere near it). Is this OK?
- I don't quite understand why I need to separate the ground and neutral at the subpanel. My main panel has the two bonded, so my neutral at my subpanel will still be grounded since it's grounded at the main panel. Can someone explain why this is necessary, just to satisfy my curiosity?
- How many different circuits should I be considering for these needs? I was thinking 1 for the 5HP planer, 1 for the 5HP shaper, 1 for the power feeder (And future power feeders), and 1 15A for the 2 1.5HP shapers, as they will never run at the same time.
- Is there anything else I'm missing or overlooking?
I'd like to start working on this expansion by the weekend, so your advice is very much appreciated.
UPDATE: I purchased https://www.lowes.com/pd/Eaton-40-Circuit-20-Space-100-Amp-Main-Breaker-Load-Center-Value-Pack/3027588 which comes with two neutral bars bonded together with a strap. Am I allowed to simply remove the strap and use one of the bus bars as a ground bar, or do I need to purchase a ground bar kit separately? Additionally, the panel came with a small piece of bent metal that attaches one of the bars to the panel. Should this be connected so that the panel is grounded?