I have a York heat pump…the condenser is coming on but the blower motor isn't. Model# F6FP030H06T3XH. My blower motor doesn't come on but the condenser does when cooling is called for. Relay is good...motor is good...transformer is good...I am getting 24v on G at control board...motor does nothing. Any ideas?
  • What's the nameplate on the blower motor say? Also, have you checked the blower capacitor? – ThreePhaseEel Jul 22 '17 at 23:45
Mark and remove the wires from R and G. Add a jumper wire across R and G. You should hear a click (that's the relay on the board) and the motor should start. If not check your capacitor (little oval device attached to this blower housing) be very careful as capacitors can give you a massive shock even when powered down. They are essentially high capacity, quick charge/discharge batteries. The rating printed on it should be around 5-10 micro farads. The reading on your multimeter should be within 1 of the printed value. Also check for power output of 120v on the fan terminal (most likely low cool with G jumpered High cool with Y jumpered) on the board with your other lead to ground. No 120v on the high or low cool terminal with R jumpered to G, your board is fried. Yes 120v your capacitor or motor is fried if the cap is good and the motor is bad change the cap and motor together.
There are elements to this diagnostic that are potentially harmful and should not be done by the average DIYer. Hopefully it's the cap. Easy and cheap fix.
| improve this answer | |
  • Hello, and welcome to Home Improvement. Four answers in two hours: you're really jumping in, and with good information, too. Keep 'em coming, and thanks. – Daniel Griscom Feb 14 '19 at 17:49
When I had that situation with my Carrier system the HVAC tech replaced the entire control board and the blower worked again.