3

I had another question about the electricity in my shed that I now understand, but in one of the comments:

Either this is a real oddity (a split bus QO) or a severe Code violation (MLO panel improperly used as a main panel with no service disconnecting means)

Outside

power comes into the house

The Panel

no cut off- inspected plumbing though

Behind the Cover

so many wires, but no main cut-off breaker

Top of the Panel

top of the panel

Main Panel Inside (Closeup)

inside of the panel

Bottom of the Panel

the bottom of the panel

In the bottom here you can see the thick black wires coming in through the back punch out on the left side.

On the right side you can see the large bare aluminum wire in the clamp by itself - this goes out the wall and is connected to the grounding rod. That actually didn't exist until our mains power was shorting with the ground and our electricity started swinging wildly from 80v-240v, which caused the power strip we had under our bed not only to trip, but the capacitor(?) melted/blew up and it started arc welding itself. That was an exciting way to wake up from a nap. But there was no option to just flip a main breaker and cut the power, so I just had to do it manually.

So, what is up with my panel? Is this normal? Was it at least a legal thing to do in the 1970's when my house was built?

7
  • If you turn off the far top left breaker, do any of the circuits below the two gaps in the panel's breaker loadout have power? What does the far top left breaker feed, even? Commented Jun 30, 2017 at 23:48
  • Also, how many amps of electrical service do you have? Commented Jun 30, 2017 at 23:55
  • Not sure how many amps, how would I tell? Commented Jul 1, 2017 at 15:39
  • You may have to call your utility on Monday and ask them -- please tell us what that top left breaker controls, though. Commented Jul 1, 2017 at 20:57
  • So apparently I was wrong, but I'm not sure how it works - that top left breaker actually does shut everything off. Commented Jul 3, 2017 at 21:28

3 Answers 3

3

Your real problem is a lost neutral.

That's why your voltages were going all 80-240V. The neutral wire broke between the panel and the pole. This needs to be fixed. Unless it's in your panel, it's the power company's problem and should be reported as a power outage, which it actually is. Shut off everything until it is.

If hooking up a ground significantly improves conditions, that diagnostically proves the neutral problem, but This is NOT a legitimate or safe fix!!! It should not be continued for even one more minute. Shut Everything Off and get that neutral fixed.

Since your panel does not appear to have a main breaker, you would need to call your power company and have them come out and pull the meter. They need to do that anyway to investigate the lost neutral.

Now might be a good time to get a meter pan which contains a main breaker. I would obtain it and have it ready for when the power company comes out to fix the neutral. They may just fit it for free, since they're in there anyway, and replacing beats troubleshooting.

Other stuff

The nice thing about a main breaker on the meter pan is if you turn it off, your entire panel is deenergized, which makes the panel safer to work in, and makes a whole-panel replacement safe to DIY. Not that there's anything wrong with a QO panel! It is small for my tastes.

However I think you definitely do have a split-bus "rule of six" panel.

Fill the empty hole in slot 28 with a spare breaker. They make proper blanking plates, but I find them flimsy and expensive, and breakers are cheap and a heck of a lot easier to find. Label it N/C.

The zinc plated copper ground wire is fine. You can't use aluminum for ground wires.

The big aluminum is fine and in fact preferable, since the lugs are aluminum. Beware of small gauge (12-8 gauge) aluminum wire in the house on branch circuits. That is the scary stuff. Until recently, the repair approach was to run around screaming and tear your hair out, then tear your wire out. Today, there's a magic device called an AFCI breaker which will catch arc faults, which is what we're worried about with aluminum wire. That, with CO-ALR terminations or Alumiconns, I'd sleep well at night.

It's definitely a Rule-of-Six "split bus" panel.

Now, the dead giveaway of a Rule-of-Six panel, look at the top 12 spaces (where the six Rule-of-Six 2-pole breakers go). Follow all their wires. Are they all accounted for? NO. Breaker 1's extra fat wires do not leave the panel.

Its top wire does a most unlikely thing, that seems like an optical illusion but is not: it goes straight down, just to the left of the L1 lug. Look close in empty position 9, you can see it again just left of the bus, with that same spackle splattered on it. And just to the right of the L2 lug is an equally fat wire that is mostly obscured, that can only be its partner. Split-bus panel.

Now look at Space 14, right side. Compare to spaces 28 and 30. See how the bus is different there, as in weirdly missing? Split-bus.

I'm not a fan. I would transform any Rule-of-Six panel into a Rule-of-One panel by having only one breaker in the Rule of Six area. QO makes snap-on breakers as large as 200A that will fit there, then I'd feed an external subpanel. (the internal subpanel is too small).


** If you really know what you're doing, you can activate certain loads, e.g. 240V-only loads (which have no neutral).

0

This isn't a "split bus" panel.

It is a standard "Main Lug Only" panel that is illegal to use as a main panel. It can be used as a sub-panel but not as the main.

See if you can find a main breaker add-on kit to fit it. I doubt you can since the deadfront does not have a knock-out for a main breaker. But it is worth looking.

Otherwise, the panel should be replaced by a normal main-breaker panel. It might be feasible to transfer just the guts from the main-breaker panel into this enclosure and use the new deadfront. That's way you don't have to remove and replace the whole enclosure.

Good luck and stay safe!

0

I agree with ArchonOSX this doesn't look like a split panel. The answer to your question is no this was not code (NEC) in 1977 unless the meter base had / has a breaker. Back in the 70's and 80's it was no problem to pull a meter to do maintenance and call the power company then they would swap the meter and put a new seal on it (sometimes just a new seal). I put in quite a few service panels for older homes that way. Your area may have been lax on code adoption/enforcement they are currently on the 2014 code according to the NEC 15 June 2017. You should have a main disconnect and I would question the house wiring if no breakers tripped when the MOV's in your power strips were shorting (that's how they limit power spikes). I have worked on homes in the past that have bypassed the meter for a portion of the house (s) some had breaker protection some did not.