Can I enclose the wiring inside PVC that is for electric?

It will run on the outside of a garage. I am running 50 amp 120 volt wiring for my RV hookup from the breaker box to the end of the garage on the outside with the proper size wire (8 gauge) 22ft.

closed as unclear what you're asking by Tester101 Jun 28 '17 at 13:04

Please clarify your specific problem or add additional details to highlight exactly what you need. As it's currently written, it’s hard to tell exactly what you're asking. See the How to Ask page for help clarifying this question. If this question can be reworded to fit the rules in the help center, please edit the question.

  • 1
    Are you asking if you can use PVC conduit? It's done all the time. What specific question do you have? Please edit to clarify. – isherwood Jun 27 '17 at 18:46
  • 2
    How did you arrive at 8 gauge as the wire size for 50A? – Harper Jun 27 '17 at 20:52
  • 1
    You need at least 6 Ga copper or 4 Ga aluminum for NEC ampacity sizing. Hint - the aluminum is a LOT cheaper. And your standard 50A RV plug is 120/240, not 120 volt. – Ecnerwal Jun 27 '17 at 22:11
1

Yes, PVC is made for this purpose. If it is an area exposed to vehicular traffic and could be struck by a car you should consider schedule 80 PVC.

Otherwise, schedule 40 is the standard for outdoor electrical.

A 50 amp RV plug should probably be 240 volts though.

Good luck and stay safe!