I have had really low water pressure. I have a 3 year old Sta-rite 1/2 hp jet pump and a 30' deep, 12 fixtures and a house built 12 years ago.
I get about 3 mins of decent pressure then the pump kicks in and the pressure drops considerably. I was told going from a 20 gal pressure tank to a larger tank would give a longer duration of decent pressure. I installed an 86 gal tank, and it did almost nothing, better pressure but for the same amount of time. I spent over $450 installing the new tank..How do I fix this?
It was a pre charged unit, I didn't install or change the pressure switch, the piping is cpvc after the pressure tank, bronze from the pump, galv from the point to the pump
  • What's the plumbing made from? Galvanized, CPVC, copper, PEX/PEX-AL-PEX? Commented May 29, 2017 at 17:22
    "better pressure but for the same amount of time." That sounds suspiciously like you also altered the pressure switch settings, if there's "better pressure." Or possibly that you bought a pre-charged tank and did not adjust it to your system pressure. If the new tank is 4 times the size of the old one, and the pressure and prefill settings are the same, there would be 4 times as much water there.
    Commented May 29, 2017 at 18:26
  • Also are you confusing pressure and flow rate? While related, they are not the same thing.
    – Tyson
    Commented May 29, 2017 at 19:10
Water storage in a pressure tank is a function of what pressures it swings between as well as size. The most storage for a "common" setting is at "20PSI on / 40PSI off" - for the usual pressure switch that has a fixed 20 PSI differential, water storage reduces as you move to 30/50, 40/60, 50/70. A setting lower than 20/40 is not normally used. One 86 gallon tank I'm looking at has a capacity of 31.8 gallons liquid at 20/40, which shrinks to 23.2 at 40/60. The 20 gallon tank in the same series is 7.4 and 5.4 gallons at the same pressures, so something is clearly wrong with your installation if you have no increase in capacity.
Since you mention better pressure, I see one of two possibilites -
  1. You (or a plumber) altered your pressure switch setting as well as changing the tank.
  2. You bought a tank that was pre-charged to a pressure above your lower working pressure and did not adjust it when installing on your system.
In the latter case, the tank stores essentially no water below the pre-charge pressure, so it will run out and pressure will drop precipitously - but what water is stored will be at a higher pressure. This would match up with your perception that the pressure drops as the pump kicks on.
To resolve - Set your pressure switch to 20 on, 40 off, assuming it is the typical 20PSI differential, adjustable setpoint switch. Turn the pump breaker off when adjusting the switch, as the mechanical and electrical parts are often under the same cover.
With the system turned off and water drained, set the air pressure on the tank to 18 PSI (2 PSI below the cut-in, if you decided to change the setting to something other than 20/40.)
Or - simply record what the pressures are when your pump starts and stops - then drain the system and set the pressure tank air pressure to 2 PSI below the start point. It seems unlikely that your pressure switch is so far mal-adjusted that you'd see no capacity increase, so I'm leaning to an over-pressurised tank as the most likely situation for the conditions you describe.
Incidentally, if you have not discarded the 20 gallon tank and it's still in good condition, you can connect it to the system for additional capacity.