I'm trying to wire my kitchen up to code, which means (based on the outlet spacing rules) I need 6 counter-top outlets. How many branch circuits do I need?
When the NEC talks about the 2 "appliance" branch circuits required to be installed on kitchen counters, it says in 210.52(B)(1), the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A) and then immediately follows that with:
210.52(B)(2)
No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electrical clock in any of the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
I can see two possible ways of understanding "other outlets" in context, and I don't know which is correct:
- It could mean, "Outlets besides the receptacles 210.52(B)(1) described aren't allowed on the appliance branch circuits," in which case I could do however many receptacles can be on a circuit normally.
- But it could also mean, "the appliance branch circuits must have exactly one outlet each," in which case all 6 outlets would need to connect directly to 6 individual breakers in the panel.
Which is it?