So, I'm planning the installation of both a 50A RV outlet and an adjacent 20A GFCI 110v outlet on the back wall of my residence. I have separate 50A and 20A breakers and will use 6/3 and 12/2 romex respectively. Running the wire completely indoors to the intended location appears to be next to impossible so I want to poke the wires out of the dwelling and run the last 10' or so outside. I have obtained 3/4" non-metallic flexible conduit for the purpose and have the appropriate weather resistant 1 & 2 gang boxes and in-use covers for outlet installation. My question is this: can I run the two conductors together in the conduit to their respective receptacles as-is or must I strip their outer insulation for the balance of the run that is within the conduit?

  • Are you talking about LFNC, ENT, or some other product when you say "non-metallic flexible conduit?" – ThreePhaseEel May 17 '17 at 1:42
  • "Conductors" is a synonym for "wires". The 6/3 and 12/2 are actually cables which contain several wires/conductors each. – Harper - Reinstate Monica May 17 '17 at 2:34
  • When I say 'non-metallic flexible conduit' I mean: lowes.com/pd/… – Somnambulator May 17 '17 at 3:25
  • Yes, I understand 6/3 has 4 wires and 12/2 has 3 (ground wire included). I just want to know if I need to strip the romex or can run them both in the conduit whole. – Somnambulator May 17 '17 at 3:27
2

Romex can't go outside

You would have to use cable rated for outdoor use, such as UF type.

Alternately, while you are in conduit, you could simply use the correct single-conductor wire, i.e. the very common THWN-2.

This is really pushing the limits of 3/4 conduit

3/4 conduit, supporting THWN single conductors, can support four 6 gauge conductors, fullstop. No more room for anything else.

Couple pieces of good news though. You only need a 10 gauge ground, and it can and better be bare for space, and you can share the ground with the 20A circuit. So you need three #6, two #12 and one #10 bare. Someone more code-geeky than I will have to tell you if that's legal in 3/4 conduit, but it's really pushing it.

The trouble with "pushing it" with conduit is it makes the pulls really hard. It can either become a miserable afternoon, or force you to hire an electrician for the pull. And he won't touch it with a 10 foot stick of EMT unless everything you're doing is code perfect. Because he has to sign off on all of it.

Ease of pulling is a big deal for the DIY'er, and that is why I usually oversize my conduit by quite a bit. Conduit is cheap.

Can't use wires without the cable sheath

They lose their physical protection, and they also lose their markings. You can't use random unmarked wire. It loses the weather resistance of UF. You also can't pull shucked Romex or UF through a conduit, the insulation isn't tough enough to survive the trip. When you see THWN wire this will make sense.

You would be unable to pull 6/3 UF through 3/4" conduit, let alone with another cable too!

Wires through a hole in your house must be protected

There needs to be some sort of appropriate protection, like a conduit or cable which is rated for this use (and remember it needs to be outdoor cable too).

If it were me...

I would use a short non-flexible conduit as a liner, with a junction box on both inside and outside. The inside junction box would be a fairly large one, the outside could be a simple conduit body.

At the inside junction box, I would transition from Romex (Indoor rated NM) to THWN-2 wires. Outdoors I'd travel in ahem 1” or 1-1/2" rigid conduit, which looks pro and needs far fewer attachment points to the building. And since I have plenty of space, I'd give each circuit its own ground wire. That would be me.

  • I'd go with 1.5" (1.25" I believe isn't quite as easy to find as 1" or 1.5" -- and as you said, bigger conduit isn't exactly a big hit on your wallet :). Otherwise, good answer! Also, can I go back in time and thwack the first guy who said you had to shuck cable to stuff it down a conduit with a paper copy of the NEC? – ThreePhaseEel May 17 '17 at 3:43