There is an outlet in my place that tests ok but when I plug in anything, it doesn't power up. The tester I'm using is a three light tester.Actually, I've used two testers. Both of them indicate the it is correct. What gives??? Anyone have an idea?
    It may be a broken wire or faulty back stab connection. It is possible to light the neon lamps in the tester but with a load the wiring opens. I have seen this in the past and tho problem may be in a prior outlet If part of a daisy chain.
    Apr 21, 2017 at 18:49
    @EdBeal that's pretty much the answer I would write. Apr 21, 2017 at 19:12
    Comment answers are a pox on SE. :) I never know whether to write basically the same thing in order to resolve the question or wait around for the commenter to do it and get credit.
    Apr 21, 2017 at 19:21
  • Ed and Harper, Thank you for that answer. I did not know that about those testers. I thought those were the best thing since buttered bread.
    – Steve M.
    Apr 21, 2017 at 21:57
The three-light testers typically only draw a tiny current and usually use neon indicators that work at less than full voltage. They are good for showing a few common miswiring problems (e.g. where live and neutral have been swapped or where ground is not connected) but they are not good for showing bad connections which have a high resistance or which separate when hot.
I would turn off the breaker, verify power is off at the outlet and open it up and check the connections. The next step would be to swap the outlet with a new one or with another nearby working outlet.