4

I am trying to raise the voltage to 240 V so that I can power two computers with 1300 watts, each on ONE 15 ampere circuit.

I power four 15-A circuits in my shop via a 60 ampere breaker I keep in my main panel. I came ought to that 60 ampere breaker with three #6 wires (two hots + neutral) and a #10 ground.

Each of my PCs is 1300 watts.

So, all I need to do is wire the existing neutrals that are already on the bus bar (those neutrals which originate from each applicable circuit. In my case, the only ones on the bar), remove these from the bar, and place the neutral in another 2 pole 15-A breaker. Is this right? Will this allow me to connect 2600 watts to one circuit? Is all I need to do to add a two-pole breaker and move the neutral to it?

  • 3
    Did you actually measure their draw, or is this estimate based on the PSU sticker rating, because that's a terrible way to size loads. – Hari Ganti Apr 10 '17 at 18:40
  • 9
    Actually, most modern PSUs auto-sense voltage and can operate on either 120V or 240V without a physical switch. – user4302 Apr 10 '17 at 19:27
  • 4
    The NEC requires receptacles of differing nominal voltages to be of different configurations. The receptacles would have to be changed so someone doesn't try to plug in a 115 volt device into what appears to be a standard receptacle and start a fire. – ArchonOSX Apr 10 '17 at 20:04
  • 2
    @JDługosz Assuming you live in America, which apparently, most people do not. – Aron Apr 11 '17 at 3:24
  • 2
    @R.. in the original edit, OP described it specifically as a mining rig. Someone changed that to PC for the reason "removed pointless rferences to cryptocurrency". Perhaps not so pointless after all. – Harper - Reinstate Monica Apr 11 '17 at 23:07
28

Hire an electrician before you burn your shop down with all those computers in it.

While I can try to educate you, the fact that there's PLENTY of information already available and yet you clearly have done no research or just don't understand your power system makes the above my succinct advice.

In short, neutral has nothing to do with a 240V (only) circuit in the USA/Canada system.

You replace two 15A one-space breakers with one 15 amp two-space breaker, and both legs are hot. You need to replace the receptacles on the circuits as well.

Alternatively just add 4 more single-pole 15A breakers and wire new 120VAC circuits to them.

Please hire an electrician rather than forge ahead half-understanding; or take a good long time to actually understand before you touch a wire.

  • 2
    The first sentence shall be engraved in stone! – Crowley Apr 11 '17 at 9:03
  • 2
    @Crowley actually I think the last sentence is more universally applicable and timeless ;) But either way you splice it, the moral of the story is the same: don't screw with electricity unless you are damn sure what you're doing! – Doktor J Apr 11 '17 at 17:05
  • @DoktorJ: The moral story is universal, no need to stick just to electricity only. I cannot see any difference between a case your house burns down when you turn lights on or your hous fall down because of butterfly landing ontop your roof... – Crowley Apr 12 '17 at 6:51
  • Ecnerwal, I appreciate you coming by. Your advice reminded me of something I told a customer once. This is good general advice I have been known to often disperse to certain DIY'ers. I have to apologize to everyone - the next question I ask will be further researched, without a doubt. I must have come off as green in my original post, but I actually did some electrical work at a nonunion shop for about 18 months - me and another guy redid the Baton Rouge Airport rotunda expansion. Almost all of my experience lies in the commercial side, however. – Norman Dunnagan Apr 12 '17 at 23:15
  • Trick being that in commercial work you just need to build what's on the drawings, and someone else probably figured out what you need. When doing for yourself, you need to do that part, and you need to not get casual about it because you happen to have some largely unrelated experience. I suspect your best option here is to add 4 more 120V circuits (first, understanding that a 60A double-pole subpanel feed is perfectly capable of running 8 15A single-pole breakers, not limited to 4.) – Ecnerwal Apr 12 '17 at 23:35
5

The loads

The "1300w" power supplies for PCs are apparently a specialty item made by a few manufacturers. That nominal wattage is the power it can give to PC components; due to inefficiency, it draws more from the grid.

A PC doing heavy computation is what's called a continuous load. For those, you must allow an extra 25%. For instance if the load is 12 amps (1440 watts), then 125% of that is 15A. Now, 15A is the common circuit size found in houses, and power supply manufacturers know that. The power supplies are designed to draw 12 amps because of this rule.

The ones I studied are switching power supplies (required so they can hit the "Gold" power factor), and they can also run on 240V. At twice the voltage they take half the current, or 6A. Two of those (12A) will "max out" a 240V/15A circuit when you account for the 125%. Another common size is 20A, but three will overload a 240V/20A circuit, so there's no benefit to going 20A.

The rules generally prohibit putting multiple receptacles on circuits larger than 20A. If you're feeding a bunch of machines off a 60A breaker, nope.

240V on the 15A circuit

If you are in a dwelling unit, they do not allow 240V circuits unless absolutely necessary, i.e. A load is over 1440W (the max for a continuous load on a 120V/15A circuit). As discussed, these power supplies are exactly that so they don't qualify. But that's OK, you have plenty of power in that 60A split-phase service.

If you are not in a dwelling unit, you can do as you propose: pick a circuit, change every load and receptacle to 240V, mark all the white wires with tape to designate them as hots, and punch them down to a 2-pole breaker rated 15A. You could then plug up to two of these PCs in 240V mode. You must use a 240V receptacle and get 240V cords for the PCs. Do not under any circumstance wire 240V to a common 120V receptacle, that would create a booby trap for anyone else who tried to use the receptacle!

240 receptacle 2-pole breaker

These receptacles are also made in "doubles" like the normal double receptacles you're used to (with the blades different obviously).

60 amps on 6 AWG wire

This is OK. 6 AWG wire is good for 55A at 60 degrees C temperature, however since they don't make 55A breakers, you can go up to the next size, 60A.

Making the most out of 60A/240V with neutral

You mentioned "4 circuits" so you may have already done some of this. You cannot simply hang a bunch of 120V/15A receptacles off a 60A split; you need to have a sub-panel.

Now imagine you get an 8-space sub-panel and fill it with eight 15A/120V breakers, and use those to feed eight 15A 120V circuits. Can you do that? Yes you can, because of your neutral. You have 60A on each leg of the 240V, so you have 60A/120V on one side, and 60A/120V on the other side, both at once. It will work fine.

This will let you serve eight PCs.. That is more than what you need.

Get a panel with plenty of extra room, like a 20- or 30-space, or even 42. It costs a bit more, but they often give you free breakers. And it'll be nice if your needs ever change. Your breakers equal your capacity only because you plan to load everything to 80% of max. In normal loading you could have more than 8 breakers.


Of course, the problem with this sort of activity is the power company makes most of the money. However some power companies offer plans that give you power almost for free if you play their game right... That can change the finances of mining.

  • All good, save for the notion that you can't put multiple outlets on a >20A branch circuit. (You can, you just need to use right-sized receptacles, save for the 40/50A case, where you actually can't power anything but cooking appliances from it if you're in a dwelling unit. Strange, if you ask me...) – ThreePhaseEel Apr 11 '17 at 1:10
  • If he's in a residential dwelling and can't install a 240VAC outlet, then isn't this a good application for a MWBC? (though he'd have to pull another wire for it). He can plug one power supply into each half of the circuit. – Johnny Apr 11 '17 at 18:59
  • @Johnny definitely, if he has 2 hots and neutral already in the cable. I was under the impression he did not. – Harper - Reinstate Monica Apr 11 '17 at 23:01
  • Harper, thanks for the post, now I understand things better. I owe you one, and also this was a learning experience. The next time I write a question, I won't rush and will word it better so that we'll all be on the same page. Thanks again all who responded. – Norman Dunnagan Apr 12 '17 at 23:21
1

All I need to do is add a 2 pole breaker and move the neutral to it?

AIUI (I'm not an American so I may have missed something) to do this properly you need to.

  1. Ensure all equipment you plan to connect to the circuit is suitable for 240 V operation.
  2. Disconnect the hot and neutral wires of the circuit from the breaker and neutral bar and connect them to a new double pole breaker. The former neutral wire is now a hot wire.
  3. Change the receptacles on the circuit to NEMA 6.
  4. Mark the former neutral wire red at both ends so that people know it is a hot wire.
  5. If the equipment uses a voltage switch move it to the 240 V position.
  6. Replace the plug or power cord on the equipment to connect to the new receptacles. For appliances with IEC power cords I would suggest marking the appliance end of them somehow so you know at a glance which IEC connectors have 240 V on them.
  • I would add that you should get a receptacle tester to make sure everything's wired correctly. I'm afraid I can't find one that's appropriate for the job, because google's giving me prioritized search results for UK vendors, but you're looking for something like this except for a 240VAC circuit rather than 120VAC. – Jules Apr 10 '17 at 20:56
  • Hi Peter, thanks for the input. In some of my friends' setups, they have the 240v setting on 120v receptacles. It will be good to do this the right way, the first time! Thanks for the post. – Norman Dunnagan Apr 12 '17 at 23:32
0

This is probably not the answer you are looking for, but in the interests of preventing house fires:

  1. Please always specify what country you are in, so that you can be advised appropriately of local wiring codes and legal restrictions (and so your audience knows whether you have 110V or 230V mains).

  2. If you plug in any set of non-faulty appliances of any sort and a circuit-breaker pops, that means you should consult a qualified electrician unless you are very sure that you know why that happens, what can be done about it safely, and whether you are legally permitted to do that for yourself. (In which case you probably don't need to ask questions here). A circuit breaker is there to stop the wiring in the walls of your house from an overload, consequential overheating, and setting the house on fire. If a breaker pops, consider that to be a house fire averted. You probably need a wiring upgrade to support what you attempted. You may be under legal constraints as to what you may do for yourself.

  • No, I'm looking for all kinds of feedback and it is all much appreciated. I was an apprentice electrician for several years, I know how to take criticism. Guy who taught me used to throw my 1/2 pipe back down at me if he didn't like my kicks. Best teacher ever. – Norman Dunnagan Apr 11 '17 at 19:45

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for?Browse other questions tagged or ask your own question.