I have a commercial building which will have retail outlets I know it is 2 layers of 5/8 drywall for the ceiling what is it for the walls do I have to use 5/8 or can I go with 1/2 for the walls

closed as unclear what you're asking by isherwood, ThreePhaseEel, Ed Beal, Tester101 Apr 6 '17 at 16:32

Please clarify your specific problem or add additional details to highlight exactly what you need. As it's currently written, it’s hard to tell exactly what you're asking. See the How to Ask page for help clarifying this question. If this question can be reworded to fit the rules in the help center, please edit the question.

  • 3
    You should probably call your local building inspections office. (You haven't even told us where you are.) – isherwood Apr 5 '17 at 17:51
  • 1
    What type of wall are your referring to? If it is the occupancy separation walls, they are typically determined by what level of fire separation that is required. If you're meeting a fire rating, the entire wall assembly needs to be considered as a whole, which will determine what all of the components used to make that wall will be and their combined rating. If it's interior walls within one occupancy, then that is an entirely different scenario. – pdd Apr 5 '17 at 18:04
2

If the entire facility has fire sprinklers, then it doesn't matter, unless there is a "sound rating" requirement. Otherwise:

For 1-hour WALLS use 5/8" Type X (fire code) gypsum board on each side.

For 1-hour CEILINGS use 5/8" Type X (fire code) gypsum board on bottom of joists spaced up to 16" oc with fire rated assembly on top. (If it's an attic, you'll need fire rated roofing on fire rated assembly.)

For 2-hour WALLS use 2 layers 5/8" Type X (fire code) gypsum board on each side. Stagger the joints in the gypsum board both ways (horizontal and vertical) and use approved nailing pattern (length and spacing). Also, there are requirements about extending it beyond the edge of the building too.

For 2-hour floor-ceiling assembly they are not available for wood construction (cut timber) only for steel trusses, concrete joists, etc. and fairly difficult.

Exterior walls are not required to be fire rated, only "party walls" unless you are within the setback area from the adjacent property line.

As you can see, this is very complicated and you'll probably need some professional help from a local architect. By the way, you can't do the work, unless you are a licensed contractor in your state, even though you own the building. Bummer.

  • I think it depends on the state for licensing requirements. I believe GA allows owner-building for business buildings. But there might be a distinction between "business use" and "commercial classification". For example, a farmer can build a store to sell fruit on his own property. (A lot of times it comes down to what you call the building on the permit paperwork.) – Nick Feb 10 '18 at 1:57