I am building an RV campsite at the bottom of my property to live in while our house is under construction. The RV requires a 50 amp service. I want to install a 100 amp sub-panel down there to give power to my RV, and future gate opener for our driveway entrance. The run from the main panel is about 350'. I will need single phase power, a ground, and a neutral down there. What size copper wire do I need for 60 Celsius since it is under 100 amps, and that length of run?

4
  • For a single 240V supply you might want to think about a 60A panel as you will probably never be close to the 50A load on the motor home unless you have dual AC, and a dryer (Mine ran in the mid 40 amp range fully loaded) a 100 amp load at that length would need 3/0 wire where a 60 amp load would only be #1 copper. The gate closer won't don't draw much power but I did need to run the AC with the dryer running in the summer. here is a voltage drop calculator so you can play with the numbers. 3% or less is your needed voltage drop.
    – Ed Beal
    Mar 28, 2017 at 14:11
  • 1
    OP, I need to know whether you want 120V or 240V at your 50A. It matters a LOT. You can do this with much less wire cost than your numbers are telling you now. I'll give you an answer tonight when I have some time. Mar 28, 2017 at 16:26
  • The standard for motor homes is 30a 120v. / 50a 240v
    – Ed Beal
    Mar 28, 2017 at 20:23
  • It took me a few minutes to find the code reference NEC 551.46 , however the actual voltages listed are 125 / 250.
    – Ed Beal
    Mar 28, 2017 at 20:40

2 Answers 2

3

This isn't a shopping channel, but unless money is no object, money will rear its ugly head. So I will heavily price the options, based on prices from random USA big-box stores. (and these are "by-the-foot" prices for the wire, a whole 500' spool may be cheaper.)

How deep do you want to bury this thing?

This is a factor. The expensive rigid conduit only needs 6" deep burial, the cheap PVC conduit needs 18". You can (in some sizes) buy direct-burial wire that must be buried 24". That's a lot of trenching for 350', consider the cost difference there. The cost of conduit also interlocks with the thickness of wire, as smaller wires need smaller conduit. As some examples of cost for conduit alone:

  • $300 -- 2" PVC conduit legal to bury 18" deep
  • $1400 -- 2" RMC conduit legal to bury 6" deep
  • $1200 -- 1-1/2" RMC conduit legal for 6" deep (barely worth the savings)
  • $500 -- 3/4" RMC conduit legal for 6" deep

Before you rush to use the minimum size conduit, price the next larger size. This will make wire pulling a lot easier, which means you are less likely to get stuck and need to call an electrician for the pull.

Do you really need copper? How big a deal is voltage drop?

People often go to copper by default, or because of "problems they hear about". That was never an issue for large cables like this. The fact is, large-wire lugs are made of aluminum. The cost of copper is insane, and nobody buys direct burial cable in it, anyone splurging for Cu also splurges for conduit. I'll price both ways and add conduit to the Cu pricing.

Voltage drop: Realistically your RV will rarely use 30A and almost never use 50A. The "conventional wisdom" is to size for 3% voltage drop of your realistic usage (30-50A). However some people nonetheless spec wire for 3% voltage at absolute max current capacity (100A). Your call. Assuming the latter:

  • $3600 -- copper 2/0 conductors (#1 ground) in 2" PVC conduit (buried 18")
  • $1340 -- aluminum 4/0-4/0-4/0-2/0 MH feeder cable (direct buried 24")
  • $1700 -- aluminum 4/0 conductors (2/0 ground) in 2" PVC conduit (buried 18")
  • add $1100 if you'd rather bury rigid conduit 6".

Size voltage drop for actual use

Now if you want to size for 3% at 50 amps, and 6% at absolute max 100A - so a 7V drop on a 120V circuit - you can save some coin. Unfortunately I could not find direct burial cable in these sizes, they would expect you to bump up to the above sizes, or use conduit. So we shall.

  • $2750 -- copper #1 (#3 ground) in 2" PVC conduit (18" burial)
  • $1400 -- aluminum #1/0 (#1 ground) in 2" PVC conduit (18" burial)
  • add $900 if you want to use Rigid conduit buried 6" deep.

Transformers

When you increase voltage, transmission losses drop dramatically. Just for chuckles, let's look at using transformers to kick up the long-haul transmission voltage to 480V. Now you want 240V at 100A, which is 24,000 watts, or 24 KVA. 24 KVA is 50 amps at 480 volts. To contain voltage drop within 3.3 percent, you'd use

  • $560 -- #6 copper direct-burial UF-B cable (buried 24")
  • $500 -- two copper #6 wires in 3/4" PVC conduit (buried 18")
  • add $500 for rigid conduit buried 6".

25 KVA is a common transformer size. With aggressive shopping/deal-hunting, you can find 25 KVA 480V transformers for $300-400 each. With two of those, the total bumps to $1100-1800. Much as I love to throw this option in, this one is a wobbler - is the slightly lower cost worth the added complexity? On the other hand, it sure makes the wires and conduit small!

Keep in mind you are not running neutral or ground, in fact, your two 480V wires are entirely isolated from the electrical system at both ends. This isolation causes your remote site to be separately derived service, thus a *main service" and the panel there will be a main panel.

0
1

The RV has a NEMA 14-50 plug, right? Which means you'll need four conductors (hot, hot, neutral, ground). Using 2/0 copper would keep the voltage drop below 3% @ 100 amperes.

VD = 2 * 350' * 100A * 0.0000967 ohms/ft. = 6.769 volts.

If you wanted to use aluminum, you'd have to use 4/0 to keep it below 3%.

However, if the loads are not going to be anywhere close to 100 amperes, you could definitely use smaller conductors. If you figure the maximum load closer to 70 amperes, you could use 1 AWG copper, or 3/0 aluminum.

It really depends on your load calculations, and what type of power quality you're looking for.

Alternatively, you could install a transformer near the site. This would allow you to supply the transformer with a smaller circuit, but still get the power you need at the RV.

It also might be possible to have a second service installed near the site, but that would depend on the site and the utility.

2
  • 1
    LOL 1400' of 2/0 Cu is like $4000 worth of wire. This is why you don't do that thing that way. I'll think about alternatives, soon as I can find my big spool of 14AWG and a couple of transformers! Mar 28, 2017 at 16:04
  • 2
    @Harper I didn't say it was a good idea, just answered the question.
    – Tester101
    Mar 28, 2017 at 21:59