I have touch operated light switches operating LED lights throughout my home. The switch manufacturer claims that I must add a device to circuits containing LED bulbs of 5w or less to prevent flickering. They show their device connected between the neutral and hot wires before the driver and after the switch. Some of the devices "popped" - they suggested to replace the device with a 5w 100k ohm resistor bridging the hot and neutral wire before the LED driver and after the switch. Does this make sense? Is this correct? Is this not a short circuit when the switch is on? photo from light switch company
    I'm actually very surprised that you would be adding a resistor... Also, if the devices "popped," they aren't likely resistors, or if they were, then whatever the manufacturer is telling you to replace them with is likely to "pop" again. It would make more sense to add a filter capacitor to help debounce the switch when it switches, but a capacitive switch shouldn't have that issue in the first place. I believe there is much more going on here than it initially appears. Perhaps the resistor will work, but I've never heard of this practice, and it seems sketchy at best.
    – Hari
    Commented Mar 21, 2017 at 17:56
  • @HariGanti this appears to be the ole' dimmer-on-LED problem. The resistor side is 230V. Commented Mar 21, 2017 at 18:00
  • @Harper This seems different, but I don't know enough about what the problems with LEDs and dimmers were to say anything for sure. I tend to stay away from non-PWM dimmer switches anyway.
    – Hari
    Commented Mar 21, 2017 at 18:07
  • @HariGanti that being the problem. I don't know what that box does, but the red-red side of it is 230V according to OP. I suspect the puck lights are indeed 12V and this would be worlds easier if he was simply working in 12V directly. Commented Mar 21, 2017 at 18:09
  • @Harper Yeah, though I'm not sure the voltage matters (as long as the LEDs are rated for 230V systems). The passive components (ex. capacitors, resistors, and inductors) are insensitive to voltage, within their maximum limits. The reactive components only respond to frequency changes, and resistors really don't react to much at all because they're linear components. I strongly believe in LV circuitry for non-A19 LED lighting.
    – Hari
    Commented Mar 21, 2017 at 18:26
First, you are not allowed to use electronic components in mains electrical wiring. You must use "equipment" which has been tested and certified (listed) for use in mains electrical wiring. Equipment may simply be an electronic component in a safe housing built to a certifiable spec and run through the independent testing lab to test for fire and health safety. TUV or UL are testing labs, CE is not.
A resistor is a resistor, as long as it is made for this purpose and the ohm values are within 50-70%. If Moon Rune Importers there can't provide a Listed resistor, get a resistor from another manufacturer.
If that doesn't work for you, change the smart switch to one that does not have the resistor requirement. Electronic ballasts/drivers are not a surprise. CFLs have been on the market for over 20 years, governments have been expressing their intent to deter/ban incandescents for almost that long, to warn manufacturers to stop making things that aren't compatible with electronic drivers. So they have no excuse.
A 100k resistor on 110/120V will draw as follows:
E=IR   120V = I * 100,000ohm    I = 0.0012 amps
W=EI   W = 120V * 0.0012A       W = 0.144 watts
A 100k resistor on 220/230/240V will draw as follows:
E=IR   230V = I * 100,000ohm    I = 0.0023 amps
W=EI   W = 230V * 0.0023A       W = 0.529 watts
Either approach seems reasonable. I'm not sure where you get a 100k resistor that's listed for use with mains electrical, but 0.5 watts is little enough energy that cooling won't be a big factor.
It will be a short, as you suspect, but it won't be a dead short. Current will be limited to 0.0012 amps or 0.0023 amps, depending on your voltage. This will result in watts of power consumed being under 1 watt.
The only thing that surprises me is that such low current flow would suffice.
10
  • Hello,thank you for quick answer - pardon me - it is 220v system. The light switch manufacturer recommended I add the resistor.
    – keyarc
    Commented Mar 20, 2017 at 8:28
  • @Harper Resistors aren't rated for voltage, only power, so any resistor is capable of being used in an AC or DC system of (almost) any voltage. The only real exception is when you near breakdown voltages for the carbon medium in most resistors.
    – Hari
    Commented Mar 21, 2017 at 17:57
  • @HariGanti -- resistors actually are voltage rated. You need to get a 2W or bigger resistor of a flameproof type (typically) in order to get something with sufficient voltage rating for across-the-240V-mains. Commented Mar 21, 2017 at 22:21
  • @ThreePhaseEel I've got to disagree with you here... Again, there is the practical limitation of the breakdown voltage, but aside from that, for a typical carbon-film resistor, you simply need to stay below the power rating. I've used ordinary CF resistors to over 400V.
    – Hari
    Commented Mar 22, 2017 at 0:30
    @HariGanti -- yeah, it's not terribly hard to get the right voltage rating once you have power dissipation squared away. I'm just pointing it out because there are resistors where voltage rating is...more critical. Commented Mar 22, 2017 at 0:55
The resistor you talk about provides an alternate path for a small amount of current -- these "smart" touch switches apparently use the short-cut of trickling power through a turned-off load in order to power themselves. (Apparently the smart switches only need a couple mA of current, hence the large resistor value used.)
A capacitor is a better solution
However, because of the power dissipation required by a resistor, the more typical solution to the "trickle current" problem with LEDs is to use a load capacitor to provide an alternate path for the small amount of current required by a smart switch. In fact, Lutron makes just such a capacitor as the LUT-MLC, and it's UL listed for use on systems running anywhere between 120 and 277VAC, making it usable basically the world around.
If you really want to use a resistor...
If you really want to use a resistor for this, the resistor will need sufficient wattage (1 or 1.5W) and voltage (500V) ratings, and also must be mounted clear of combustible materials (in the US, NEC 470.3 specifies a 12" clearance from combustibles) as it will get toasty-warm in operation. Temperature rises of 70 or more degrees C can be expected for the resistor in question despite the low current draw.