I am building a floor to house the water cistern, future electrical power generator, and propane gas tank in the far back corner of my house. The main water line comes from the front of the house and I'll need to tap it for the cistern. The most pressure is about 65 PSI. I am thinking of digging a trench along and close to my wall to all the way back, which is about 90 feet.

I want to maintain 3/4 inch inner diameter for my water lines. I was thinking of using Schedule 40 PVC tubing for the water line and return. I know cooper is better but it would be way too expensive. I need to add another pipe for the electrical for the future generator and power for the water pump. Not sure how thick that pipe would need to be. I guess I have no choice to use cooper for the gas line.

I want to do the trench, water pipes, and leave the electrical pipe in the ground for the electrician. Maybe leave a rope in the electrical pipe to save the electrician some time.

I live in the Caribbean so there is no real winter. Can I dig a trench and put the water pipe in, water line return, electrical pipe, and gas line in the same trench? How deep and and wide should I dig my trench? What other types of tubing would you recommend that isn't too costly but durable?

3
  • What all materials are authorized by Code for potable water and gas where you're at? Mar 20, 2017 at 3:55
  • Coding here is pretty much a joke. That said, I have no idea. I'll stick to whatever US national code.
    – Rick
    Mar 21, 2017 at 0:06
  • You can also bury PEX. I haven't heard great things about CPVC from people who work with it, but PEX seems to work fairly well. You can even reduce the number of fittings you'd need because its flexible.
    – Hari
    Mar 21, 2017 at 1:57

1 Answer 1

3

Materials selection

There are three materials that you can practically use for a buried potable water line: CPVC, PEX/PEX-AL-PEX, and copper. Of these, PEX is the easiest to install, while copper is the most proven in-service, with CPVC being a middle ground. While there is straight PVC that is used for utility water service lines, most PVC pipe readily available is DWV (drain-waste-vent) pipe that is not approved for potable water service. (If you doubt me, Tables 605.3 & 605.4 in the 2015 IPC refer to different standards than tables 702.1 and 702.2 regarding PVC pipe.)

As to the propane gas line, you must contact your gas supplier for acceptable materials. If you can't get a response from them, Schedule 40 or heavier black iron with joint compounds labeled as suitable for all gasses always works. (The Code approval for copper in gas applications depends on the amount of sulfur in the gas, and using plastic for gas lines requires lots of special work that renders it infeasible for anyone but a gas utility. See NFPA 58 and NFPA 54, as well as the 2015 IFGC, for details.)

Last but not least, you'll want to lay conduit for the electric lines instead of a direct bury cable. In a co-trench situation like this, I would use a nonmetallic, physical damage rated conduit such as Schedule 80 PVC or RTRC-XW. Direct burial of metallic conduits is also possible, but offers little advantage over PVC given the issues with corrosion a buried metal conduit faces, unless you use red brass that is, which is extremely costly compared to PVC.

If you must use a direct bury cable, PVC jacketed MC-HL is recommended as it provides enhanced damage protection and leakage current control compared to a standard MC cable's interlocked armor, although it can be harder to find. Do not bury an unjacketed metal-armored cable, or NM for that matter!

Trenching

The minimum trench depth for a gas line is 12", and the same is true for water lines where freezing is not a concern. The electrical, though, must be deeper (either 18" or 24" deep), so that sets your trench depth. Width is not critical save for being able to properly install the piping with due concern for expansion (especially for CPVC pipe and rigid nonmetallic conduits).

As always, make sure to excavate safely -- call your local One-Call or equivalent utility marking facility before you dig!

2
  • I've been reading on PEX for my water lines and like the idea. Is it ok to put both 3/4" PEX lines inside a 2 inch Schedule 40 pipe to protect them? What type of PEX should I look for? Most will be underground except the last few feet that will be exposed for the cistern connections. Only cold water will be going through and probably no more than 70 PSI running through.
    – Rick
    Jul 30, 2017 at 17:41
  • @Rick -- look for PEX that's certified to NSF 61 and NSF 372 as well as ASTM F 2023 -- PEX-A vs PEX-B is merely a minor manufacturing difference. Sleeving is optional, but can be a good idea to make future servicing either; make sure the PEX inside has room to expand though! Jul 30, 2017 at 18:09