My wife and I just moved into a new house that was built in the 1930s. There is a mixture of two prongs and three prongs, but there are no three pronged outlets in the most ideal places (I.e. my desk or bedside). How much work is needed to get a few of the two pronged outlets changed to three pronged outlets?

Also there is an outlet I have never seen before, could someone tell me what it's for?

Photo of outlet

  • Cost is off-topic and will vary considerably depending on what your wiring is behind the outlets. The pictured outlet is a 240V outlet most typically for a heavy duty air conditioner – Ecnerwal Mar 6 '17 at 15:49
  • Are you asking how to replace your outlets, or how to install grounded circuits? – isherwood Mar 6 '17 at 15:53
  • For reference, here is a chart of outlet types: stayonline.com/reference-nema-straight-blade.aspx – Sean Jul 24 '17 at 19:42
2

If you only have one or two places where you need three-prong receptacles, you don't have to figure out which is "first" (nearest the panel). The NEC (since at least 1987) also allows you to replace ANY ordinary, non-grounding (two-prong) receptacle with a non-grounded, 3-prong GFCI receptacle. Marking it as having "no equipment ground" was added as a later requirement, as mentioned by Ecnerwal.

1

Use the GFCI loophole

There's a rule (and for very good reason) that if its two supply wires have GFCI protection already on them, you can fit a 3-prong receptacle there even though it doesn't have a proper ground. GFCI prevents electrical shocks by detecting ground faults; power taking a route it should not. This is not quite the same as a full and proper ground; so for instance if you touch a metal chassis and get a spark of static electricity, that has nowhere to go.

Receptacles are typically wired in a string, like the larger screw-base Christmas tree lights. The 2-wire cable goes from the service panel, to the first receptacle, to the second, third and so on. It's important to know which receptacle is first on that chain.

You can fit a GFCI receptacle at that first location. The rest of the chain can be attached to its LOAD terminals, giving them GFCI protection. They will need stickers saying "GFCI protected". Then you can change them to 3-prong outlets. They cost about $3 for a decent one (avoid the 60 cent cheapies). Then you'll need to stick "no equipment ground" labels on all those receptacles, and "GFCI protected" labels wherever that's not obvious.

If you don't want to sort out which one is first, just change the circuit breaker to a GFCI breaker. These are more expensive, and they also prevent you from fitting a simple AFCI breaker. AFCI detects arcing and sparking from wiring faults; left alone they will start a fire.

Use the ground-retrofit rule

The 2014 electrical code threw open the door to retrofitting ground wires. It is debatable whether grounds are as good as GFCI for life safety... but they complement GFCI's very well. And of course they help protect equipment from static and lightning.

The new rules allow you to leave the existing wiring alone and simply retrofit a ground wire using any practical means. You don't need to run a ground all the way back to the panel, or even follow the same circuit paths as the wiring. You only need to reach any existing ground wire, provided that wire is thick enough and goes back to the same panel. So for instance you can hang off a range or water heater cable, or the one going to that nice NEMA 6-20 receptacle in your photo.