0

I have two lights and a split receptacle wired like so:

enter image description here

Now I want to wire a second switch into the room, but I'm having trouble working the split receptacle into the mix. I feel as though 3 conductor cable isn't going to cut it. Am I going to have to run more than one cable? Or can this be accomplished using only one cable run between everything?

The switches are going to be at opposite ends of the room from everything.

4
  • Which box are you running the cable from the new switch to? Also, is /4 NM available where you're at? Mar 6, 2017 at 4:48
  • @ThreePhaseEel I'd probably have to go sopping for it in the city, I doubt they'd have it in and of the local stores here, but I could probably order it. If there's a way do do this with 4 conductor cable I'd be interested in seeing a wiring diagram.
    – ShemSeger
    Mar 6, 2017 at 5:18
  • Is this related to your other question where you have a light in a stairwell? In a stairwell, you should have a 3-way switch at the top and bottom. Those switches should only operate the luminaire, and nothing else. If you want to use a split receptacle, that switch should be on its own. It can be put into a 2-gang box with one of the 3-ways. Mar 10, 2017 at 15:47
  • Pics of your actual space would help a great deal. It seems like there are details that are missing from your description. Mar 10, 2017 at 15:48

2 Answers 2

2

If the switches you are using are typical switches and not the new techno type gizmos which require neutrals, then all you need to do is replace that switch with a three way switch and add a second three way where you want the second switch to be. Pull a piece of Romex (3 conductor cable with ground) between the two switches.

Use the red and white in that cable as travelers between the (2)- 3 way switches and the black as your switchleg. That black wire in that cable will terminate underneath the black screw at your new switch location but tie into your wire feeding the lights/receptacle ('red wire in your drawing') at your switchbox that you already have in place.

The hot feed (in your drawing above) will terminate underneath the black screw of the three way switch installed at that box.

Remember, put a piece of red or black tape on the white wire in the cable so that others servicing the box down the road will know that white wire is not a neutral wire.

2

Don't even try.

Just do what you're already doing, to one of the switches. Then, run a /3 cable from that switch to the other switch.

At that point, it's the common, standard "both switches on the end of the string" 3-way circuit. Simple enough.

Use /4 cable

Or, do exactly the above, except -- oh wait. The receptacle. Nevermind.

This idea would work if the second switch is at or past the receptacle. In this case red remains switched-hot, and black-blue become messengers. Feed black/always-hot to the nearer 3-way, past that it carries black-blue/messengers to the other switch, which returns it on red.

It would also work if you could install conduit in that section where the messengers must parallel the always-hot. You can't buy /5, but you can put 5 wires in conduit.

Heck with it. Smart switches.

Since you've done such a nice job of busing always-hot, switched-hot and neutral, this situation is ripe for a pair of smart switches.

You would need a pair that communicates via power-line signaling or by wireless/radio, since you have no spare wires. Unless you'd like to do the kaboodle in /4, and use blue for the signaling wire.


Addendum: What about running 2 parallel Romex cables, i.e. /2 and /3 instead of /5? No, no, no! It is vital that in every condition, the current outbound be in the same single cable as the current returning. AC current emits a formidable, magnetic field pulsing at 50/60Hz (which is how transformers work.) When the outbound current and returning current are in the same cable, these fields substantially cancel each other out. However if they are in different cables, anything between them gets the full brunt. This causes eddy currents and magnetic heating (this is the reason transformers are laminated). Also, EMF is literally electro-motive force, meaning it wants to make things move. (which is how motors work). Two separate cables could move/vibrate/buzz relative to each other, damaging or fatiguing the cables over time.

1
  • The OP should be able to fix this situation without the use of anything more than 3 conductor wire, and basic switches. It seems like there are a bunch of details left out of the description. Mar 10, 2017 at 15:49