A home inspection claimed a gfci outlet tripped and would not reset when testing with a receptacle tester's test button. When I looked into this, what happens is that this is tripping the circuit breaker. This outlet is on a 20 amp circuit with an Eaton ground fault breaker type CHGF as shown in the attached photo labeled basement bath.
Other outlets for which the tester does not trip the breaker are on 15 amp circuits with an Eaton combination type AFCI, type CHAF breakers.
Is there a problem with this behavior of the circuit breaker being tripped by the tester, or is that normal for this type of circuit breaker?
  • Your photo didn't go through (thankfully, it's not necessary to answer the question) Feb 26, 2017 at 5:22
GFCI tester test + GFCI = tripped GFCI
A CHGF is a GFCI and circuit breaker in the same package, using the same breaker contacts and trip mechanism. So, when your inspector pushed the test button on his receptacle tester, shunting a bit of current to ground, the GFCI-breaker saw the difference in current between hot and neutral generated by this and tripped, just like it was designed to.
This also means you don't need to connect a GFCI receptacle to that circuit -- it's silly and redundant at that point, and also leads to the coordination problems you're seeing where two GFCIs are tripping in reaction to the exact same ground fault. Thus, the easiest way to solve this is to replace the GFCI receptacle on that circuit with a regular receptacle with a "GFCI Protected" label on its front and let the GFCI breaker do its job. (If you want a more permanent solution than label maker tape, then Legrand and Leviton make permanently stamped/pre-printed wall plates.)
(P.S. a more reliable test of a GFCI is to use the "test" button on the unit -- that shunts current from load-side-hot to line-side-neutral, which will also trip the GFCI, but does it independent of any problems with the equipment ground to the outlet.)
  • 4
    Agreed. It's just facepalm-silly to have a GFCI device feeding another GFCI device. But we see this classic blunder all the time, and the home inspector is super dumb if he doesn't recognize it. The seller probably begrudgingly installed the GFCI receptacle on top of the GFCI breaker because he got a violation on no GFCI in the bathroom. Actually, the violation was lack of a "GFCI protected" sticker on the plain receptacle. Feb 26, 2017 at 6:30
  • @Harper -- good catch Feb 26, 2017 at 8:27