5

I would like to run 50 amp service to my garage. The run is about 100 feet in total. About 60 feet will be in the basement, 20 feet in conduit attached to bottom side of wooden deck floor joists, and the remainder in conduit buried. Is this feasible? If so, what size and type wire do I use? Does the wire running in basement need to be in conduit? If so, what size & type? When it goes outside, what size & type conduit do I use? Please see diagram attached. Thank you for your assistance.enter image description here

2
  • Are you running the service at 120V or 240V? (i.e. one hot leg or two?) Commented Feb 17, 2017 at 23:31
  • I'll be running 220v Commented Feb 21, 2017 at 12:45

1 Answer 1

4

This is quite feasible to do

The hardest part about a job like this is getting your wires down the conduit. Even with that, though, I would use conduit for the full length of the run to keep things simple. Schedule 80 PVC is likely the easiest and best solution for a mixed indoor/sheltered/buried run like yours -- it is rated to protect wires against physical damage, is weatherproof, and assembles much the same way that PVC plumbing pipes do (i.e. with cemented joints). Just keep three rules in mind:

  1. PVC will do the worm on you due to thermal expansion if you don't put expansion joints in every 12' or so in the exposed (i.e. not buried) parts of the run.
  2. Conduit needs support -- for PVC, attach it to the wall or deck joists every 3' and at expansion joint locations.
  3. Keep the number of bends between pull points to a minimum. Code only allows a single loop (360 degrees), but less is better -- you can use conduit bodies to change direction and reset the bend-count at the same time, provided they're accessible later.

Once the conduit's in, along with a pulling-string to help you get those wires in it, it's time to get some conductors in there. You'll need THWN wires as the conduit outside is considered a wet location, and four of them at that: two hots, a neutral, and a ground. The neutral must be white, and the ground must be green or preferably bare to save conduit space, while the hots can be any other color than white, green, or grey. As to size, you're looking at 6AWG copper or 4AWG aluminum for the hots and neutral, and a 10AWG copper wire for the ground.

Last but not least -- you'll want to size the conduit generously, and a 1.25" PVC conduit will easily fit 3 4AWG aluminum wires and a 10AWG copper ground with room to spare. Of course, if you want to put in a bigger conduit, knock yourself out -- it'll pay dividends if you want to upsize the wiring or pull more conductors later.

4
  • I'm sure that you are right, but I thought that the ground wire had to be able to carry (at least) the current of either of the hot phases. Would you point me to the code section so I can brush up?
    – bitsmack
    Commented Feb 18, 2017 at 0:01
  • @bitsmack -- Table 250.122 is what you're after. Commented Feb 18, 2017 at 0:16
  • I'll be running 220v Commented Feb 21, 2017 at 12:44
  • +1 - but I'd suggest going well beyond the minimal 1.25" conduit size: you never know when you may need to rerun something. Go as big as you can afford (within reason) now - much much easier than having to replace the conduit later because something happens and you can't run anything else because it's already "full"
    – warren
    Commented Feb 21, 2017 at 18:16