Got a wifi thermostat. Behind the old thermostat was a blue "C" wire. The other side of the blue wire in the equipment room isn't plugged into anything. I need to get the 24v common hooked up to this blue but don't know where it goes. Any help is greatly appreciated.
diagram
wires
The wiring diagram you posted is quite clear on what it wants you to do; namely, it wants the C wire connected to the furnace chassis ground. To do that, simply drill/tap a 10-32 hole in a suitable spot on the furnace chassis if there isn't one present already, screw a premade ground pigtail into it, and nut the C wire to that pigtail.
10
  • I could simply unscrew the Chassis Ground (there is a screw that already has a blue wire from the condensing unit going to it) and put this blue wire there and screw back in. I don't think I would need to drill a new hole. I'm not following how this would provide constant power to a smart wifi thermostat..... if I am hooking it up to a ground, how it is getting power? Feb 15, 2017 at 23:43
  • @user3330299 -- the thermostat already has the 24VAC side in the form of the R wire, you just need to close the circuit with a C wire to provide a return path for that juice besides through the furnace board :) Feb 15, 2017 at 23:53
    While technically this will work, it's not exactly the correct way to do it. By connecting the C wire to the chassis, you're effectively using the chassis as a current carrying conductor. I guess it's only possibly ~1A @ 24V, but still. It's like telling somebody to connect the neutral to the ground on a receptacle, and you wouldn't do that, would you?
    – Tester101
    Feb 16, 2017 at 13:45
  • @user3330299 If you know anything about AC wiring, you can think of the R wire as the ungrounded (hot) conductor, and the C as the grounded (neutral) conductor. In the furnace, C (neutral) is bonded to ground (the frame). So connecting the neutral from the thermostat to ground, gives it a path back to the source (albeit and inappropriate path, in my opinion).
    – Tester101
    Feb 16, 2017 at 13:49
    @ThreePhaseEel that's likely because the manufacturer doesn't want installers messing around with the factory installed wiring. It's an accepted practice in the HVAC industry, but in my opinion it's a bad practice. Telling the OP to connect the thermostat C to the same chassis screw as the condensing units C (using properly sized ring terminals), would have been a bit of a better answer. Telling the OP to willy-nilly ground the wire to the chassis, is not so great (while technically acceptable). I mean what are we, the auto industry?
    – Tester101
    Feb 17, 2017 at 11:57
  • If there's a C terminal on your board (can't tell from picture), use that.
  • If you have an air conditioner, it will have two wires that connect back to the thermostat (usually via the furnace): so long as one is going to R, the other will be C and you can splice into the same spot.
  • Lastly, you can splice into a wire from the transformer. You'll need a multi-meter to figure out which one it is (measure 24V between the C side of the transformer and the R terminal).
    • It does look like common is grounded to the chassis, so you can also use that to identify the side of the transformer -- find the side that has a wire connected to the chassis.
    It'll be one of the bottom two terminals:
Test
You should use the multi-meter to test -- no matter which method you use -- before you actually splice into anything.