I am wiring a luminaire fixture through a short dedicated 1/2" EMT conduit (a couple of feet). The maximum rating on the luminaire is 100W, although I expect to use much lower wattage. What is the minimum gauge wire I am allowed to use? Am I allowed to used something smaller than 14AWG in the conduit (say, 16AWG)?

  • 1
    I think you have to maintain 14 until you are actually AT the luminaire, but I'll defer to one of the usual suspects. – Ecnerwal Feb 7 '17 at 22:40
2

You're logicking out that since the lamp can't draw more than 100W, a smaller wire size should suffice. That is covered under the tap rules.

Metal conduit is required because the lamp could suffer a fault condition where it pulls too much current for its tap wiring but not enough to trip the breaker. For instance if you had a 14AWG tap off a 125A circuit, and then had a 75A fault.

But this is all pointless if you can't find 16/18/20 AWG THHN which is actually cheaper than 14 AWG, and you probably can't.

Not least, because NEC does not allow wiring smaller than 14 AWG on any branch circuit. Some cities have local ordinances increasing it to 12 AWG.

Within equipment is a different story, e.g. the interconnections within a chandelier.