How do I make a 3 wire splice with 2/0 wire? I want to tap into a service panel feed to add a subpanel.

5
  • What is enclosing this splice, or is it a direct burial application? Jan 20 '17 at 2:35
  • Also, are you splicing copper or aluminum wire? Jan 20 '17 at 2:49
  • 1
    Usually done with large split-bolt connectors, or "gurneys". Kinda sounds like this would not be a "subpanel", if you are tapping into the wires feeding the service panel. It would be another service panel, no? Jan 20 '17 at 7:14
  • Not a fan of the split bolts. You have to smother them in electrical tape, and that makes them hard to inspect. I agree something is odd; this is only used in rare and specific situations, and I would have expected him to mention that. These little short tweet-sized questions leave you wondering. Jan 20 '17 at 7:26
  • 2
    I don't like the sound of this at all! You DO NOT simply "tap into" the service panel wires. You put the sub-feed conductors on a circuit breaker. Jan 20 '17 at 12:30
1

Are you sure this is the right thing to do? It's rather unusual. If you are feeding a subpanel from a main panel, there would be no call for doing a 3-wire splice, you put a circuit breaker in the main panel and feed the subpanel off that.

You would only use a 3-wire splice off the top of the panel in the rather unusual situation of having 2 panels of equal rank; i.e. two main panels. The new panel would never be called a "subpanel" unless the panel you're tapping off of is already a subpanel. And the panels would be right next to each other. In those cases, you'd use either screw-down splice blocks, or dual lugs.


It's difficult to infer skill from a question the size of a tweet. What concerns me is that you have the common case of adding a subpanel to a main panel, and you are freestylin' because you know that little about how this stuff works. I certainly hope not.

You use a breaker that snaps into the regular breaker spaces below the main switch, and you feed the subpanel off that. It may be quite a large breaker, which may necessitate moving even more circuits. Don't same-pole any MWBCs (and if you don't know what that means and why, you are out of your depth, and no, googling MWBC won't complete your knowledge.)

enter image description here

3
  • Your answer is spot-on Harper, but I'd be wary about including the second part, about splicing. Nothing about the over-simplified original question sounds correct. Simply adding double lugs to a main panel is almost never the right thing to do. Jan 20 '17 at 12:33
  • CO/ALR is only for wiring devices -- the equivalent rating for terminals is AL7CU or AL9CU Jan 20 '17 at 12:43
  • @SpeedyPetey you are quite right. Emphasis changed. Jan 20 '17 at 16:03