2

I have an older furnace and am looking to add a c wire for a smart thermostat. Currently behind my thermostat I have red/black wire, however, there are 3 additional wires that are not connected.

At the furnace the red/black are connected (as shown below) and the 3 additional wires are free.

From what I understand the C wire is 24 volt common. I have metered the furnace running/not running and found a post transformer wire that is 24 volt constant. Can I simply connect one of the spare wires to this terminal or is there potential for too much of a current draw blowing the transformer?

enter image description here

Red coil wire is from thermostat. 24v constant is the bottom right black wire (this is where I want to connect the C wire to)

2
  • What's the model number on that gas valve?
    – Tester101
    Jan 13, 2017 at 11:36
  • VR800C 1190 is the model number
    – user65052
    Jan 14, 2017 at 20:41

1 Answer 1

2

Yes, the terminal at the lower right in the photo is C.

Here's the wiring diagram from the documentation, which I highlighted in different colors.

enter image description here

Here's your wiring, which I highlighted using the same colors.

enter image description here

1
  • Thanks! I will connect one of the spare wires to the TR and then to the C slot on thermostat.
    – user65052
    Jan 15, 2017 at 3:58

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge that you have read and understand our privacy policy and code of conduct.

Not the answer you're looking for? Browse other questions tagged or ask your own question.