I'm looking to use a piece of commercial equipment in my home, and I've been reading about AC current and circuits. I currently have access to an old style non grounding 10-30 style plug, which I understand is unsafe to adapt this device to plug into, because it has no ground.

I've been reading that during normal operation, current is supposed to use the neutral as a return path, and in the event of a neutral fault, ground is supposed to become the return path, which trips the breaker. My question is, if the 6-20 plug doesn't have a neutral, and only has two hots and a ground, doesn't that mean that the ground wire is used as the return path, and the stainless enclosure of this appliance is ungrounded?

How is this safe?

EDIT: The outlet I currently have is for an older dryer, and is a NEMA 10-30. The plug for the new device is a NEMA 6-20p, and it's for an induction cook top.

3
  • Is this for a United States application (for code and practicality purposes)? Jan 12, 2017 at 18:00
  • Yes, this is in the United States.
    – jakogut
    Jan 12, 2017 at 18:06
  • I'm not the person who would answer, but making it clearer which is a 10-30 and which is a 6-20 would probably be helpful. Jan 12, 2017 at 18:24

4 Answers 4

2

I've been reading that during normal operation, current is supposed to use the neutral as a return path

While that statement is correct, it is also incomplete. Think about it this way.

A US standard 120 volt circuit is like a guy cutting down a tree using a hack saw. The guy is the live wire and he delivers power to the device, the saw. The neutral wire is the empty space on the other side of the tree where the saw sticks out; if the empty space didn't exist then the saw couldn't move.

A US standard 240 volt circuit is like 2 guys cutting down a tree with a saw that has handles on either end. Both guys are live wires pulling the saw, but taking turns. Their movements are out of phase. No neutral is needed because when one guy is pulling, the other guy is pushing.

enter image description here

and in the event of a neutral fault, ground is supposed to become the return path, which trips the breaker

No. This is wrong. It sounds like you've incorrectly summarized what can cause a breaker to trip, and the purpose of a ground wire.

  • Overcurrent: If too much current flows out of a breaker, it will trip.
  • Ground fault: If the current flowing out of the breaker on the live wire does not match the current flowing back in through the neutral, then it must be going somewhere else, like through you. That will trip a GFCI breaker or device.
  • Arc fault: When a wire breaks, it can cause a spark. If the wires remain close enough, a continuous spark (or arc) can be maintained. Arcs send out radio frequency noise that can be detected at the breaker, which will then trip.

The purpose of the ground wire is not to cause a trip, but to instead provide a better path for the electricity to flow if, for example, the case of a metal appliance become electrified because of a broken wire. Since your body presents a higher resistance to electricity than a copper wire, the ground wire will take the majority of the current, thereby sparing you the brunt of the shock.

2

NEMA 6-20 (hot-hot-ground) is for 240v circuits not requiring a neutral. Some motors or perhaps a heating element.

If a neutral is required for the equipment you wish to connect you cannot use the NEMA 6-20 configuration.

1

NEMA 10-30 is a 125/250 volt 30 ampere connector without a ground, consisting of two hot and one neutral conductor.

NEMA 6-20 is a 250 volt 20 ampere connector with a ground, consisting of two hot and a grounding conductor.

To answer the question you asked... No. If there's no neutral, the current will only flow on the hots. unless you connect the neutral from the equipment to ground, in which case you're doing it wrong.

Without knowing what the equipment requires, there's no way to tell you what you need. Just to put it out there, NEMA 14-30 is a 125/250 volt 30 ampere connector with a ground. If the equipment requires two hots a neutral and a ground (120/240V), you're going to want to use a connector with four terminals (hot,hot,neutral, ground). If the equipment only needs two hots (240V), you can use a connector with three terminals (hot, hot, ground). If the equipment requires a 30 ampere circuit, you're going to use a connector that's rated for 30 amperes.

1

The neutral is for returning current for circuits which need 120V in part or in full. It is not required for 240V machines. It has nothing to do with an equipment safety ground.

In other words, neutral is not ground. Neutral is just another conductor. It has a different name than "hot" merely because it happens to be near ground potential.

The presence of ground is what you should consider safe.