5

This is on the inside of the panel door. panel info

The box says that my panel it is UL Listed for Siemens and Murray breakers.

I see the table on the bottom for Main Breaker and Branch Breakers. But I still find it hard to search for the breakers. I'm looking for compatible AFCI breakers online...for example...is this Siemens breaker - QA115AFC compatible? I see "QA" and "QAFH" in the table. I think it is because the product image shows "QAF2" However the table shows "QAF"

What about this Murray breaker - MPA115AFC? I think it is because the product image shows "MP-AT2" and the table shows "MP-AT".

Is there a better way to find these breakers?

UPDATE I'm selecting breakers and I can't find out whether to go with the 10KAIC or 65KAIC. I live in a residence and not a commercial building. Which one should I get? How do I calculate this based on the info on the panel door? We have 200 A service. I'm buying 20A and 15A AFCI breakers.

Here are photos of existing breakers. 20A breakers 200A main breakers 50A breakers to sub-panel and 15A breaker

1
  • Post a photograph of some of the breakers and any markings on them. There have been a lot of mergers and acquisitions in the business, so some companies (e.g. Eaton or Square D) have several incompatible product lines. Have to watch for that. Siemens still uses the Murray brand so if the panel doesn't say Murray I would stick with Siemens breakers. Jan 8, 2017 at 21:46

1 Answer 1

6

Match the letters

If the breaker has the same "Type" letter markings on it as are listed on the panelboard label, you're fine. Number suffixes on the type marking (such as QAF2 vs QAF and MP-AT2 vs MP-AT) are used to denote a revised type of breaker that is still compatible with the original and can be used in place of it, so they don't matter in your case.

10kAIC is fine

The Siemens/Murray line of breakers comes in three interrupting rating options -- 10kAIC, 22kAIC, and 65kAIC. The larger options are more costly due to extra internal equipment needed to break bigger arcs, and are only necessary in commercial work where larger services and feeders capable of higher fault currents are found.

In addition, in a main breaker panelboard such as yours, a breaker with a lower rating can be used because it receives a higher series rating by way of being "backed up" by the panelboard's heftier main breaker.