Background

I am installing a dimmer switch in one of the rooms of my apartment (I live in a tri-plex in California). The existing light switch works (I.E this is a upgrade not a repair). This room has a metal box, single pole, single light control. No green grounding screw or grounding copper wire (although there was a small piece of copper in the far back that may be connected to the box - which may be why the box is properly grounded).

Problem

The new dimmer switch is 1.5-2x fatter/wider than the old/traditional switch and thus both sides of the plastic casing on the switch body are touching the metal box. I have seen articles suggesting to calculate the box size needed based on number of wires but I was curios:

How much space is needed/required AROUND the switch to be safe and up to code?

NOTE: My setup is exactly as described here: http://www.familyhandyman.com/electrical/wiring-switches/how-to-install-a-dimmer-switch/view-all

2
  • The dimmer switch may have some instructions in tiny tiny print which tells you the numbers you need. Jan 3, 2017 at 18:56
  • There are shallower dimmers made for places like yours where the box is small. They are getting harder to find tho, and they cost a couple dollars more for the slimline model. Check with an electrical supply house. Wiremold also makes a box extender that gives a pretty good way of getting another 1/2" of depth. Once it's been there a week you won't notice it anymore, but it does initially look a little ugly.
    – Tyson
    Jan 3, 2017 at 21:17

2 Answers 2

1

The box fill calculation in NEC 314.16 is per device; there is no code difference in a single gang box for a switch or a duplex outlet or a dimmer. Code treats them all the same, using a 2x the wire size calculation for the largest wire connected to them.

Example: if the box has 2 cables 14 awg with ground there is a total of 6 wires but you only need to count 1 of the grounds. The metal box should have a clamp, so 1 clamp is counted at 1x and 1 device counted at 2x for a total of 8. Now we look up 14 gauge wire per table 314.16B. Number 14 wire is calculated at 2 cubic inches x 8 for a total of 16 cubic inches. The box would need to be 3x2x3.5 per table 314.16.A. I hope this helps your understanding of box fill. Note for 12 gauge wire use 2.25, otherwise the rules are the same.

Also note you need to use the listed size not a measurement of the box the above box is listed as 18 but calculates at 21.

-1

Dimmer switches generate a bit of heat depending on the wattage they're used to control, hence the aluminum heat sink that doubles as a mounting plate. You'll notice that the Lutron switch has scored tabs on the sides that can be removed if you're controlling a significantly different amount of power through the switch. These switches are also pretty bulky on the back end as well, presumably to keep high temperatures from contacting other wires in the box. You'll want to read the manual that came with the switch to see if you can trim off the tabs. The fact that the dimmer body is touching the box should not be a problem.

Newer LED dimmers, like those made by LeGrande, have fewer thermal issues and are consequently smaller.

1
  • The box fill calculation is per device there is no code difference in a single gang box for a switch or a duplex outlet or a dimmer. Code treats them all the same 2x the wire size calculation for the largest wire connected to them.
    – Ed Beal
    Jan 3, 2017 at 19:58