First off, please excuse my clunky use of electrical language. I'm not exactly sure what I'm talking about.
I recently added a 220v/30amp outlet to my garage for the purpose of an electric homebrewing system. After doing some reading, I see that it's highly recommended that the outlet be GFCI because giant pots of water + 220v is not a great combo. The garage is detached from the house and the original wiring was not easy so I'm wondering, does adding a GFCI breaker require running a separate neutral line or is it just a matter of changing something at the outlet and breaker?
  • What specific outlet type did you add to your garage? See: en.wikipedia.org/wiki/NEMA_connector – Billy C. Dec 15 '16 at 14:52
  • This is in the US, right? – Daniel Griscom Dec 15 '16 at 14:56
  • Yes, US. L6-30 outlet. – Lucian Thorr Dec 15 '16 at 14:58
  • What type electrical panel is this circuit originating from? (Brand at least, Model if you have it) – Billy C. Dec 15 '16 at 14:58
L6-30 is Hot Hot EarthGround. So no Neutral involved.
You're in luck. You shouldn't need to run a seperate neutral line.
You have two options if you want to add gfci protection to this outlet.
1) Replace the breaker that feeds it from the main panel with one that has GFCI protection. This is probably the best choice, because the protection would extend the entire distance of the buried? cable. It's the least amount of work and least expense. But it means if that GFCI trips you have to walk back to the house and go to the basement? to reset it.
gfci 30a breaker
2) Replace the outlet with a "GFCI Spa disconnect", and move the outlet slightly so that it's powered by the spa disconnect. It's rare to find a spa disconnect that comes with a 30 Amp breaker though. Most are larger.
Because you must not discard your pre-existing 30A breaker in the main panel, it would be safe to use a 60A GFCI Spa Disconnect. The GFCI capability would work regardless. Code permits the larger breaker downstream. But it might be confusing for those who come along later, so leave a note in/on the box if your spa disconnect is a higher amperage.
So If you take this option, I recommend finding a GFCI Spa Disconnect panel that does not come with a breaker, and additionally purchasing a 30A breaker for it. (Make sure its listed as compatible.)
spa gfci disconnect
3) Possible third option, do both options above. This protects the wiring between structures, as well as keeps you from walking all the way back to your basement if the fault was only local to the equipment in the Garage.
4) You may also be able to find or construct an "inline GFCI" that plugs into the L6-30 outlet and provides an L6-30 outlet. But they're going to be rare and not protect the buried cable.
GFCI breakers do not require access to a neutral to work. Only if the load requires a neutral does a GFCI also need access to neutral. If you don't intend to use a GCI breaker's neutral output lug, connect its neutral input pigtail to its neutral output lug so its obvious to anyone later that neutral is not used.
To provide Ground Fault Circuit Interruption (GFCI), all conductors intended to carry current must pass through and be disconnectable by the GFCI device.
The only reason many GFCI devices have a neutral is because 120v loads send current across neutral.
Most residential circuits are 120v only. Most residential 240v-capable outlets are actually 120/240 and have a neutral to provide the 120v service. But your L6-30 (Or any 6- for that matter) is not capable of providing for 120v devices, and this means your load doesn't use neutral. So its GFCI protector doesn't need access to neutral either.
    It's completely legal to have a large breaker downstream of a small one. The small one provides overcurrent protection (done) and the large breaker provides whatever it provides (xFCI, local shutoff etc.). – Harper - Reinstate Monica Dec 15 '16 at 17:00
  • Thanks Harper, I cleared up that ambiguity in the answer. – Billy C. Dec 15 '16 at 17:06