Country: India. Appliance: Domestic storage water heater; AO Smith HSE-SAS-006 specifications: 6 liters/2000 watts/230V~/50 Hz. My electrician has asked to procure wires and sockets for the electric/power socket installation. I have calculated the amperage requirement as 8.69~=10 amps. He has also asked for 2.5 sq mm wire to connect mains to 10 amp electric/power socket. Is this ok? My calculations: storage heater specifications: 2000 watts, 230 V. So power socket should be 2000/230= 8.69 amp. So I need a 10 amp socket. The wire gauge for the circuit should be #16~=1.31 mm= 1.5 mm. The strange thing I noticed, that the plug that came attached to the appliance is rated at 15Amp! So I will need to get `15Amp socket. But is the wire gauge ok, or should I get 2.0, 2.5 mm(wires in India are available as mm)
It is only for the circuit and socket, that will provide power to the electric heater. – Abu Galib Dec 11 '16 at 15:45
The model is AO Smith HSE-SAS-006 – Abu Galib Dec 11 '16 at 15:55
Ampacity, IECland style
The IEC equivalent to the North American NEC for low voltage (<1kV) installs is IEC 60364, and its ampacity tables are in part 5-52, Annex B. Since we're dealing with multi-conductor cable, we make the conservative assumption that it's installed directly into an insulated wall i.e. condition A2 (any other condition, such as a cable in a surface raceway, yields better cooling of the cable i.e. higher ampacity in the IEC world). Also, since the water heater in question is cord and plug connected (vs. hardwired), we assume no ambient correction from 30degC ambient is necessary.
Since this is a 15A circuit, copper wire is recommended -- aluminum is a bit fiddlier to terminate (even if it's a good alloy i.e. AA-8000 series) and offers no real cost savings for a wire this thin. PVC-insulated cable is fine here as well, unless local regulations require rubber or XLPE (i.e. thermoset) insulation instead.
Given all this, we get a rating of 14A for a 1.5mm^2 cable. If this was a hardwired heater, we'd be done. However, the heater uses a BS 546 equivalent (type M) 15A plug, so a mating 15A socket is needed, and the ampacity of the wire feeding the socket must be greater than the socket. Hence, we go up to 2.5mm^2, the next standard wire size, which gives us an ampacity of 18.5A.
So, get the 2.5mm^2 multi-wire cable.
Many Thanks! I ultimately changed the wiring from 1.5mm to 2.5mm as advised. – Abu Galib Mar 8 '18 at 15:51