I just got the results of a home inspection where they claim there is mismatched breakers and wires in my electrical panel. Specifically, the range (40A breaker) and heat pump (50A). He claims the wires are 30A.
Assuming this is true, is this a code violation (Nebraska)? Or a safety issue?
-edit- adding more info here for future readers so they don't have to read all the comments.
The heat pump had been replaced within the last 2 years. I called the company who installed it and they claim the heat pump installed only pulls 27A max but they would send an electrician out to swap the breaker that they missed. When the electrician came, he discovered that the 2nd over-sized breaker was not for the range (range was on a 50A wire with 50A breaker) but instead it was on an unused circuit that lead to the newly installed furnace (capped inside the furnace housing, just there for "future expansion"). Both breakers ended up getting swapped for free.