I have an existing 220v 50 amp plug in my garage just bought a new 40 amp Range, would like to plug in range in garage just till after thanksgiving Then will replace aa cooktop with it in kitchen can I buy a cord to match the 50 amp plug and use range over thanksgiving or will it ruin range or be a safety hazard
-
The minimum branch circuit required for ranges 8-3/4 KW and larger is 40A. They do make a 40/50 amp outlet and plug that would work fine for your range. It will not ruin your range to be on a 50 amp breaker, it will only draw what it needs. Usually there is a maximum recommended breaker size based on the range wiring but I usually install 40/50 amp outlets with a 50 amp breaker and wiring so if a high end unit is purchased at a later time the wiring can handle the load.– Ed BealNov 22, 2016 at 19:47
-
Our single oven GE range (JSP31GP) has been on a 50-A breaker for 24 years, but this question sent me to the installation instructions. They say to use a 40-A breaker and No. 8 wire! This is the breaker which the builder put in 46 years ago for the original double oven electric range with integral exhaust fan. We now have a separate exhaust fan. When we replace this range I might change the breaker to whatever is specified, but may just leave it.– Jim StewartNov 22, 2016 at 21:18
2 Answers
Using a 50A plug and receptacle is allowed on a 40A circuit because of an exception in the Electrical Code. The exception is because 40A receptacles do not exist, or rather, are not part of the NEMA standards. (There are enough varieties of receptacle already!)
The circuit breaker must be no larger than the wiring is fit for - if the wiring is 8 AWG, the breaker must be 40A (or smaller). If the wire is 6 AWG, the breaker may be 40 or 50 amps (or any value up to 50A). With large circuits like this, there is only one appliance per circuit. I am not sure whether it is legal to plug a 40A rated appliance into a circuit breakered for 50A. I would downgrade the breaker to 40A for an extra bit of safety.
This is a good time to look at the receptacle. If it's an old NEMA 10-50 type, it does not have a ground wire, and any problem with the neutral can electrify the chassis of the stove, a potentially lethal situation. A ground wire can be retrofitted using any viable route back to the panel. (Grounds don't have to travel with the conductors). Then you can upgrade the connectors to NEMA 14-50 type and change the jumper on the appliance to use a separate ground.
First -- there is no NEMA 10-40 or 14-40 plug or receptacle, only the 10-50 and the 14-50. (We already have a zillion flavors of receptacle, so why add more?) So, the Code says to use 50A receptacles on 40A branch circuits to begin with -- this is in 210.21(B) and its associated table. (Other places in the Code also use the verbiage "the receptacle rating shall be no less than the branch circuit rating".)
Second, the breaker protects the wiring of the branch circuit -- plugging a 40A range into a 50A circuit is simply a bigger form of plugging a 1A radio into a 15A circuit, something we do all the time. Furthermore, it is sanctioned by NEC 210.22:
210.22 Permissible Loads, Individual Branch Circuits. An individual branch circuit shall be permitted to supply any load for which it is rated, but in no case shall the load exceed the branch-circuit ampere rating.
Finally, do check the wiring -- 8AWG wiring goes with a 40A breaker, and 6AWG wiring with a 50A. Furthermore, the old-style NEMA 10-50s lack a ground, instead using the neutral as ground. This should be rectified, lest an open neutral cause the stove's chassis to go hot. Fortunately, the NEC allows branch circuit ground wires to be retrofitted whichever way is most convenient instead of forcing them to run with the circuit wires, so running a 6AWG wire or bare armored ground cable via the most practical route back to the panel is the easiest way to do it. Then you can put a 14-50 in and re-jumper the appliance for a separate ground.
-
@JimStewart You are correct that ranges and dryers need both 240 and 120V. The dryer wiring, BTW, is 2 hots and a neutral, allowing the motor and timer to run off of 120V while the heater runs off of 240V. Nov 23, 2016 at 20:11
-
I have a 3-wire connection for the dryer, but the heavy ground wire that leads to the panel is grounded to the cold water pipe for the washer and is exposed right next to the dryer. I could connect a wire from the ground terminal of the dryer to that gnd wire and not change to a 4-wire plug and cord. In the connection block of the dryer I would remove the neutral to chassis ground bond. Code violation? Someone could later disconnect that ground and the chassis would not be grounded. I could change to a 4-wire receptacle and connect a new gnd inside the wall or outside to the nearby gnd. Nov 23, 2016 at 22:05
-
@JimStewart -- post a new question with your situation, that way we can better help you :) Nov 23, 2016 at 22:06