Looking inside the electrical panel in the house I bought, I was surprised to see the neutral bus bar crowded right up next to the ground bus bar, so much so that it seems the ground bus bar is virtually impossible to access in order to secure grounding wires to it.

Here's a photo: Neutral and Ground Bus Bars

The neutral bus is to the left of the ground bus, and it stands slightly forward of the ground bus. You'll notice that the neutral bar is loaded with double-taps - including both neutral and ground wires. I'm not even certain there are ground wires actually connected to the ground bus (it's pretty well hidden) - though as you can see in the lower right corner of the photo, the very thick service ground wire that connects the ground bus to the plumbing and grounding electrode.

Looking at this next photo - the handling of the ground wires pictured has me asking if this is wrong and needs to be corrected?

enter image description here

Here, ground wires terminate outside the panel box, though bonded to it.

As well, a couple ground wires inside the panel box are kind of twisted together, with at least two wires wrapping around a couple of others that are connected at the neutral bar.

I have more photos of the installation, but this being my very first post, I was limited to just two. The panel box is an old Murray Class CTL Load Center, Cat. No. LC 240 PS that may date back to the 70's, when the former owners bought this house. The only information I've been able to find about what it's original intended configuration was supposed to be is a diagram on the panel door that actually shows two vertical columns of screw heads/lugs (side-by-side) that appear to represent those bus bars, numbered like the breaker spaces.

Questions, questions! Were these bus bars installed correctly? How was/is someone supposed to access that ground bus with it being so tight against both the neutral bus and the inside of the panel box? Also, I mentioned the numbering of the bus bar lugs to correspond with the breakers numbering, and so I wonder does it really matter in what order neutrals and grounds are connected to their bus bars?

overall shot of panel closeup of N/G bars twisted ground "splice" shot of breakers at an angle panel directory

2

2 Answers 2

1

If this is the only panel box, or the main panel box, then the neutral and ground wires may terminate at the same set of bus bars. This is where the neutral and ground wires are bonded together. What we might be seeing is a dual bus bar setup that is stacked and offset like stadium seating. They are likely permanently bonded together. There is no stipulation in the order of termination so long as only one wire is secured per terminal (unless the manufacturer specifies otherwise).

The ground wires outside of the box are improperly terminated. They should run into the box and to those bus bars. Look at the corrosion and dirt on that twisted mess. It most likely is not able to conduct fault current properly to trip a breaker. That's a fire and electrocution hazard right there.

Splices in the panel box are allowed so long as they are properly spliced and the total wire volume does not fill the panel to the point where you need to squeeze the cover on or tamp the wires so the cover fits.

Multiple cables through a single clamp is also a violation as the clamps are only rated to secure a single cable. The only way multiple wires can terminate to the same knockout is if the clamp is rated to do so. Standard clamps in the picture are rated for a single cable only. Multiple wires in a single clamp can slide against each other allowing them to pull out. So the dunderhead electrician tightens the clamp even more possibly damaging the cable in the process.

This is an older panel box which was built in a time where the NEC didn't stipulate more room for a panel box. Modern boxes have much more room. Tandem breakers or skinnies are allowed only if the number of circuits does not exceed the panels rating. E.g. a panel rated for 20 circuits which has 20 spaces (a 20/20 panel) can only have 20 circuits regardless of the type of breaker used. You could have 5 tandems and 10 singles for a total of 20 circuits. It can not be filled with 20 tandem breakers for 40 circuits or any combination which exceeds 20 circuits UNLESS the panel has a higher circuit to space rating like 20/40. This change was done in 2014 to alleviate overcrowded panels.

8
  • 1
    Please correct me if I'm wrong, but I believe that splices inside the box are permitted, if properly done, such as with properly-sized wirenuts. Couldn't he solve a double-tap by pig-tailing them?
    – DoxyLover
    Oct 15, 2016 at 0:55
  • 1
    First -- splices in a box are A-OK provided they're properly done and the box isn't stuffed to the gills with them (312.8), so pigtailing is a legitimate (albeit odd) way to fix a doubletap. (It certainly could be done to fix the abhorrent splice job on the EGCs at the bottom of the box.) Second -- double stuff (aka tandem) breakers are allowed still for certain in suitably identified slots on class CTL panels. (I know for sure you can get BR and HOM panels that have tandem capable slots in them.) Oct 15, 2016 at 1:04
  • @ThreePhaseEel Doh! I just reviewed the splices in the panel section. You are correct. The tandems thing I got mixed up as well. Making my changes.
    – Mister Tea
    Oct 15, 2016 at 1:11
  • @Mister Tea This is indeed the main box. I included more pics to show the entire box, more detail of the bus bars, and the "twisted" ground wires. I also included a panel door diagram that shows the numbering of the breaker spaces and the matching numbering for the bus bars. Curiously, the diagram seems to present the two bus bars as a single unit, as by its numbering of all available slots from 1 to 40 - same as the breaker spaces. But theoretically, if there were to be roughly 40 neutrals to be installed - one to a slot on the bus bar(s) - then where would the numerous grounding wires go? Oct 17, 2016 at 21:23
  • If I were to add a ground bus bar extension kit - assuming I could find one that is appropriate for this older box - what would be the proper method of bonding it both to the existing bus bar setup, and the current service ground connection? My first thought is that I'd position the extension just below the existing bar (see the top pic) - but would I use a higher gauge wire to bond it to the current bar, or use some other kind of jumper? Also, the main ground wire runs high up into the box where it attaches to the bus bar lug. Would I shorten this and attach it to a new lug on the extension? Oct 18, 2016 at 19:50
1

The "bus bars" were in fact installed correctly. It's actually only a single neutral bus bar that was pre-installed in an insulating framework. There is no ground bar.

Pulling aside some of the many wires in the panel shows a part of this framework. See the black non-metallic piece to the side of and just below the lug where the #2 aluminum Grounding Electrode Conductor (GEC) fastens to this neutral bar. The additional insulating barrier is seen folded, and extending up the side wall of the panel. insulated neutral bar

Unobscured by wires, the neutral bar looks much like this picture of one sold by Home Depot: Insulated Neutral Bar

insulated neutral bar

Referring to the last picture in the original post, the diagram shows the numbering of the 40 slots in the neutral bar, consistent with its function as a neutral bar with no ground bar present. The prior owners of the house/electricians never added a ground bar. Hence, the doubling of neutrals into the limited spaces, and the same with the ground wires.

The lower tier of slots in the neutral bar are accessed by filling that column first, sliding the wires in below the the top column. The top column would then be filled next. The included photos of crowded wiring in the top column appear to show that this procedure wasn't followed.

Referring to the photo of the full panel, you can just make out two of three pre-drilled holes - aligned vertically - on the left side of the panel's back wall. Those holes are 2 inches O.C. and will accommodate a ground bar kit made specifically to match that spacing. This is one such kit, sold at Amazon.com, made by the same maker that made this Murray panel: MURRAY ECLX075M Ground Bar Kit with 27 Terminal Positions

Murray ECLX075M

1
  • Good detective work. Looks like the previous electrician was careless. I just worked in a newly installed panelbox fully wired with MC cable. I had to add another circuit and happily found the electrician had installed not one, but two ground bars in addition to the dual neutral/ground bars which were factory installed on both sides of the panel box.
    – Mister Tea
    Oct 26, 2016 at 16:50