I'm opening up a wall between two living rooms. The wall use to be an exterior wall which runs east to west and used to have a large window which was closed up when they added the back living room. The joist also run east to west and end on a center wall and an exterior wall that run north to south.There is currently a 4x6 that ran above the old window. I've attached photo so I hope that helps. Any info on beam size or material would help. I do want to do an exposed wood design so the beam and posts won't be behind a wall.

Thanks for any info you can give me.

This is the edited one. Pic of wall

  • A drawing would make your question easier to answer. – brhans Oct 13 '16 at 19:28
  • 1
    Need more info. You are putting an exterior window in and opening between to interior rooms? unclear if the wall being opened up is load bearing or not. joists run from wall to wall? what walls? – Alaska Man Oct 13 '16 at 19:29
  • Okay so the joints from from the center beam to the exterior wall, which run north to south. I think those walls are the load bearing walls. I plan on opening up the wall that runs runs east to west. I don't think its a load bearing wall. There used to be a window there and I'm taking that out to connect the two rooms. The beam I'd like to put in is a 6x6 beam for a open beam archway connecting the rooms. The beam will be about a foot below the ceiling joist. – Mike Oct 13 '16 at 20:02
  • 1
    Your terminology is confusing. First, all joists are horizontal, so that's not helpful. Second, ceiling joists are a thing, but roof joists are not. How are the two ("horizontal" and "roof") different here? Finally, in modern construction, 6x lumber isn't used for beams, especially for spans that long. Please add new information to your post, not in the comments. – isherwood Oct 13 '16 at 20:12
1

No. 6-by lumber hasn't been used for beams since the 60s or so (and it doesn't fit in your wall anyway). An engineer would specify something between a doubled 2x10 and a doubled 1-3/4" LVL (engineered lumber) beam, up to 12" nominal height, depending on the roof system.

If I was held to the fire for a guess I'd put in a doubled 2x12 in a U configuration with a flat 2x4 on the bottom. The primary factor is whether you have a full-span engineered truss system or a conventional ceiling joist configuration where they'll be carried by the beam.

Simply put, we can't say for sure from our desks what you need, but I can say that a 6x6 isn't it. They're for posts, not beams.

Also be aware that it's not uncommon for beams that long to have twin trimmers at each end. You may also need to block through the floor system to the wall or beam below as well, to prevent overstressing the subfloor at those concentrated load points.


UPDATE:

From the new photo it looks like that wall was open at one point already. The key question is whether the opening spanned the entire width of the header. Sometimes single headers are used with intermediate trimmers acting as posts.

I'd still remove everything up to the double top wall plates and install a double 2x12 header immediately below that, replacing the 2x6 header and resting on the existing trimmers.

Disclaimer: I'm making a number of assumptions here that aren't supported by adequate knowledge of your building. You should be consulting a local engineer, not a bunch of strangers on the interwebs. Take my advice solely as a presumed plan of action to be verified before completion.

  • Thanks for the info. Sorry for the late reply but I've had a busy few day. Based on what you're both saying is that I need beam that's at least 10 to 12' high and the width isn't that big of a concern, from 4' to 6'. I would love to reroute the pipe and remove everything up to the top plates but I have look at it and there is no way of rerouting the pipe. If I need about 10 to 12 inch beam can I add a 6x6 under the 4x6 connecting them together to give me 12' total hight or are the combination of 2x12s better? Thanks for your help. – Mike Oct 15 '16 at 16:30
1

To answer you question, no a 6X6 will not carry that span, even if you have only a roof to support. The strength is in the height of the beam, not so much for the width.

In my opinion I would first reroute the pipe going through the cripples over the original header, under the top plates. After that is out of the way, then you can place the proper sized header to carry what you need.

What I did when I needed an engineer to help, I knew I was going to use LVLs so what I also knew was that the local building inspectors went by the say so of the specs given by the engineers of the company that produced the LVLs. The engineer sent me through email, a signed letter stating that such and such LVL will support my design criteria. I told him the span I needed to cover to the inch, the span of the ceiling joists on either side of the proposed beam the ceiling material, whether the attic was to be used for storage or not, which by code, that I am aware of, depends on the height of the attic or whether there is a floor present. If yours is supporting a roof load, he will need to know your area so the snow load if applicable, can be calculated in too.

So after all that and you get your beam in and it's supported properly, and since you are willing to show a 6X6 beam, dress the LVLs in a fashion that will mimic what you want in the way of a finish. It will be taller than 6", that will be the way it is, no getting around that. Of course with a little finesse you could wrap it in 1X6 on three sides and drywall the rest to the ceiling.

  • Thanks for the info. Sorry for the late reply but I've had a busy few day. Based on what you're both saying is that I need beam that's at least 10 to 12' high and the width isn't that big of a concern, from 4' to 6'. I would love to reroute the pipe and remove everything up to the top plates but I have look at it and there is no way of rerouting the pipe. If I need about 10 to 12 inch beam can I add a 6x6 under the 4x6 connecting them together to give me 12' total hight or are the combination of 2x12s better? Thanks for your help. – Mike Oct 15 '16 at 16:30
  • 1
    What I am saying and I think isherwood is too, that there is not enough info to tell you exactly what to use. You need to get in contact with an engineer, I gave you a possibility of a free one, to figure the size of beam you need. If the pipe cannot be relocated then the engineer you consult with will need to know the criteria for the beam dimension/restrictions. What you are hoping to do may not be possible. – Jack Oct 15 '16 at 17:58
  • Okay. What company did you use? Do I just email any company that makes LVLs? I'll try them and if that doesn't work try getting an engineer to come look at it. Thanks for your help. – Mike Oct 15 '16 at 18:07
  • Each vendor has their own engineer. Your engineer's letter needs to be from the same company that supplies the LVL. You should find out where you will buy the material, and who supplies it. It will be easy to do, the LVLs are usually stamped all over with their logo. – Jack Oct 15 '16 at 21:13