I need to span a beam 11' between two 6x6 posts to support the rafters for a covered pergola. I was thinking of fastening 3 pieces of 2x6 together to create a stronger piece. Is it possible?
Is there a calculator somewhere for this? I was looking at some tables, but most of them are for decks, which require higher loads than this - 10psf dead load, 5psf live load.
You can use the Sagulator. Putting in some quick numbers for Ponderosa Pine, I found a single 2x6 on edge to be acceptable for an 11' span holding up to ~1000 pounds total. Laminating 2 or 3 together will be plenty acceptable, and may be overkill, depending on the wood you're using.
  • If the load values are right for your local code. This sounds close to me + – Ed Beal Sep 28 '16 at 0:12