1

All my recepticles that are gfi except one will not reset nor will the outlets that are protected by them work? My house was built in 2006 and the receptacles are levitons. It tripped the breaker about a week ago then all of them stopped working except one. The one gfi has a crack in it. What do I need to check?

2
  • Which "one" is cracked; the one that works? Are these load fed together or are they individual GFIs? Have you tried unplugging everything that is served by them to see if it will hold? Jan 23, 2015 at 23:17
  • Have you reset the breaker? Most GFIs will not reset with the power off.
    – TomG
    Jan 24, 2015 at 3:25

2 Answers 2

1

Assuming the GFI isn't defective, there are three common things that can keep it from resetting:

  1. There is no power to the outlet.
  2. The GFI is wired in backwards: the wires coming from the breaker box are connected to the "load" side of the outlet rather than the "line" side.
  3. There is a ground fault somewhere in the circuit the GFI is protecting.

Given that the breaker tripped, (3) is very much a possibility. Alternatively, since you say there's a crack, the GFI may have been damaged.

0

I reset breaker and tried to reset and still didn't work. I don't understand why all but one quit working. Is it possible that they are all connected together?

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.