I’m looking to replace my existing thermostats (two zones) with smart thermostats that require a C-wire. The current thermostats do not have the C-wire connected, but the wire is already present in the wire bundle. I have both an HVAC system and an oil burner (Peerless WBV -03 Boiler). The oil burner has a wiring relay panel, where I can see the wiring for each zone, as well as the unused C-wire for each zone (green wire wrapped around the wire bundle). However, on the relay panel, each zone only has terminals for R and W wire connections (no C terminal). On the other side of the relay panel, there are a bunch of 120V terminals, some of them labeled as zones 1 and 2 circulators. The only two terminals on that side that are not cabled to are labeled ZC and ZR. I’m trying to figure out where I need to connect the C-wires from thermostat zones 1 and 2 to. Any help you can provide would be greatly appreciated. Please see the pictures of the oil burner relay panel I have uploaded.
1 Answer
2
-
Hi Jason, thank you very much for your feedback. I have one additional question that I'm hoping you can answer... When connecting the C-wire to the oil burner relay panel, do both the HVAC and oil burner need to be powered off at the circuit breaker panel? When I power off the oil burner, does that also cut power to the two thermostats?– JimCommented Jan 23 at 13:40
-
Thermostat power comes though the yellow and red wires in the middle picture, so if you turn off the AC supply to this box the thermostats will be powered off.– JasenCommented Jan 23 at 19:18