I have 2-2-2-4 AL SER cable running from my main panel in my unfinished basement to a sub panel in my attached garage. Since I have conduit for the last 5 to 6 feet to protect the conductors once they are on the garage wall side, information suggests I need a junction box mounted to one of the ceiling joists to splice the #2 THHN/THWN-2 wires to their corresponding conductor in the SER cable.

Using a 1-1/2 inch conduit and a straight horizontal run, tables show I need a 12 x 12 junction box. But this is larger than the width of the 2 x 10 floor joist. Is this correct?

And what is the correct method of splicing the 2-2-2-4 conductors to the the #2 THHN/THWN-2 conductors inside the junction box, do I use special connectors, or are there big wire nuts for wires this large?

5
  • 5
    Are you sure you need a junction box, and can't send the SER on into the conduit? As I've read here, it is OK to have jacketed cable like NM & SER in conduit for protection purposes if the conduit is big enough. Commented Nov 22, 2023 at 18:53
  • 2
    Cable in conduit is code legal, it's just hard to pull. However, if only for 5-6 feet of straight run, it probably won't be a major issue. At that distance, you could buy really oversize conduit to make it an even easier pull and it won't be overly expensive. If you do decide to go the junction box route, and your box is deeper than the joist you're attaching it to, it'll just stick out through the ceiling. Call it a "feature"!
    – FreeMan
    Commented Nov 22, 2023 at 18:56
  • 1
    See exceptions to 312.5(C) and skip the box up.codes/viewer/minnesota/nfpa-70-2023/chapter/3/… (MN quotes NEC) Commented Nov 22, 2023 at 18:58
  • @isherwood For box sizing I was using the formula of 8X the largest conduit when it is a straight pull through the junction box. 1-1/2 conduit = 12 in box length. Does my situation not apply? Triplefault - That was my initial approach, however what screws things up is that once I am in the garage, I have an LB conduit body to make the right angle up to the subpanel, and learned the hard way that there's no way to bend the SER cable that tightly, plus the bend radius violations. crip659 - I would love not to do a splice if I don't have to.
    – user149104
    Commented Nov 22, 2023 at 19:17
  • Could I just run conduit and THHN/THWN-2 cables directly from the main panel, then under the ceiling joists to the LB body and up to the subpanel? It's about 30 feet, all interior, and then I won't have to worry about a "rat run" board for SER cable run perpendicular to the ceiling joists, or the splice box, or the LB body bend radius. And supplies are readily available.
    – user149104
    Commented Nov 22, 2023 at 19:22

2 Answers 2

1

Ok first, you do need physical protection.

You don't need to use electrical grade conduit for physical protection. Any old thing you use is fine as long as the inspector is satisfied with it. Gas pipe, something you bend on a metal brake, you name it.

When you do use (something, possibly electrical grade conduit) for physical protection, you don't need to follow chapter and verse of the rules for using electrical conduit as a wiring method. Since it is not illegal to use cable inside conduit, you can simply send the SER on down the pipe. If there is a burr at the top of the pipe you would need a fitting or clamp, e.g. at the absolute worst a connector to pipe thread, a pipe coupler, and then a threaded cable clamp.

2
  • I didn't think far enough ahead that running SER cable through a 1-1/2" PVC sch 40 LB Body was going to be so much of a challenge.
    – user149104
    Commented Nov 22, 2023 at 22:14
  • I don't think PVC sched 40 is valid for physical protection. Maybe get some EMT of a more workable size, but 2-2-2-4 SER is 0.956" diam. so it shouldn't be impossible in a 1-1/2. Commented Nov 23, 2023 at 1:31
0

Either cable all the way, and wood or conduit for protection where needed, or wires and conduit all the way. You really don't want to splice the big stuff unless you really have to.

I mentioned wood: plywood or other wood can be used to protect the cable from damage - easy and inexpensive.