I have 2-2-2-4 AL SER cable running from my main panel in my unfinished basement to a sub panel in my attached garage. Since I have conduit for the last 5 to 6 feet to protect the conductors once they are on the garage wall side, information suggests I need a junction box mounted to one of the ceiling joists to splice the #2 THHN/THWN-2 wires to their corresponding conductor in the SER cable.
Using a 1-1/2 inch conduit and a straight horizontal run, tables show I need a 12 x 12 junction box. But this is larger than the width of the 2 x 10 floor joist. Is this correct?
And what is the correct method of splicing the 2-2-2-4 conductors to the the #2 THHN/THWN-2 conductors inside the junction box, do I use special connectors, or are there big wire nuts for wires this large?